Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Bonding of the copper supply piping

    Situation: Home is rural and on well; PVC supply piping from well to home; house supply piping is copper. Does the copper supply piping need to be bonded to the electrical system? Thanks, Mark

    Similar Threads:
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Bonding of the copper supply piping

    .Yes.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Bonding of the copper supply piping

    As always; thanks Jerry


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Bonding of the copper supply piping

    The reason is that a metallic piping system could become electrically energized. If/when that happens, a metallic piping system which is properly bonded to the ground reduces the potential for electrical shock (may not "eliminate" that potential, but reduces the potential of serious electrical shock.

    When current (including fault current) flows through a conductor (the metallic piping system becomes the conductor), the resistance of the conductor creates a voltage drop across the resistor, and that voltage drop can, depending on the voltage, cause an electrical shock (but far less than if one were to touch a pipe with a full 120 volts on it).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2010
    Location
    Ocala Florida
    Posts
    138

    Default Re: Bonding of the copper supply piping

    Yes; I was pretty sure I was right (that it should be bonded) but just needed reasurrance. Thanks again. Mark


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •