    Default Weep hole dimensions

    For vertical weep holes, what is the maximum height for the weep holes? I was thinking 2 1/2 " from BIA??

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Weep hole dimensions

    From BOA Technical Note 11B Part 3: (from here: https://www.gobrick.com/docs/default...3.pdf?sfvrsn=0 )
    E. Weep Holes:
    1. Provide weep holes in head joints in first course immediately above all flashing by: (a)
    Leaving head joint free and clean of mortar
    **OR**
    (a) Placing and leaving sash cord in joint.
    ********
    2. Maximum spacing: 24 in. (610 mm) o.c.
    3. Keep weep holes and area above flashing free of mortar droppings.

    When in that 'soldier' orientation, the 'head joint' is the full height of the soldier brick.

    Last edited by Jerry Peck; 08-27-2020 at 06:06 PM. Reason: added link to BIA Tech Note