Results 1 to 11 of 11
  1. #1
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Range hood vents to attached garage

    Microwave range hood vents to attached garage.

    Is this a breach of the habitable space / garage separation?

    Any other concerns/prohibitions other than moisture?

    Similar Threads:
    Last edited by Michael Thomas; 01-27-2008 at 11:17 AM.
    OREP Insurance
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  2. #2
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Range hood vents to attached garage

    It's wrong, dead wrong and I know that you know that. Report this dangerous defect and move on.

    Jerry McCarthy
    Building Code/ Construction Consultant

  3. #3
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Range hood vents to attached garage

    OK, supporting documentation I’ve found so far:


    Per Broan “You should never exhaust air into spaces within walls, ceilings, attics, crawl spaces or garages. The humidity and grease collect in the space.”



    FAQ

    Still a little thin though, as most microwave hoods can be configured to exhaust back into the house (kitchen).

    Nagging at the back of my mind is the suspicion that this must violate some general HVAC prohibition regarding exchange of conditioned air between the habitable space and the garage...

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  4. #4
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Range hood vents to attached garage

    OK, found it, I was looking in the wrong place:


    M1502.1 General. Range hoods shall discharge to the outdoors through a single-wall duct. The duct serving the hood shall have a smooth interior surface, shall be air tight and shall be equipped with a backdraft damper. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building. Exception: Where installed in accordance with the manufacturer's installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Range hood vents to attached garage

    Michael,

    Two guesses here:

    1) The kitchen was remodeled *without a permit* and the location was changed and it now exhausts to the garage instead of outdoors.

    2) The 'garage' was a 'carport' and was enclosed *without a permit*.

    Does either look like it may have been done?

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: Range hood vents to attached garage

    I may be wrong but I believe Michael was looking for why can't you exhaust in the garage.
    Simple answer would be draft stop.
    309.11 No duct openings in Garage

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Range hood vents to attached garage

    Quote Originally Posted by Michael Thomas View Post
    Exception: Where installed in accordance with the manufacturer's installation instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.

    Michael,

    Just verifying - that exception *does not* allow it to vent to the garage.

    I raised my post / point of view not so much to answer your question, but to get you to consider those options (if you had not already done so) as they may be larger than 'just the micro wave venting into the garage'.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Range hood vents to attached garage

    What Jerry is referring to is the venting into the garage may only be the tip of the iceberg? When folks remodel it usually never stops at one obvious defect and old timers go into "overdrive" when they sense such.

    Jerry McCarthy
    Building Code/ Construction Consultant

  9. #9
    Brian E Kelly's Avatar
    Brian E Kelly Guest

    Default Re: Range hood vents to attached garage

    All this and not counting the break in the fire wall seperating the home from the garage.


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Range hood vents to attached garage

    Quote Originally Posted by Brian E Kelly View Post
    All this and not counting the break in the fire wall seperating the home from the garage.
    Few places have ever required it to be built like a "fire wall", it was just made up of some 'fire rated' material, such as Type X gypsum board, but it was never intended to serve as a "fire wall".

    Which is probably why it is now just considered as "separation" between the garage and the living space, and that "separation wall" can have 26 gage metal duct go through it. The problem, then, becomes 'where the metal duct terminate' (the duct may only be 30 gage instead of 26 gage anyway), and it should not terminate into the garage.

    Jerry Mc. is correct: "What Jerry is referring to is the venting into the garage may only be the tip of the iceberg? When folks remodel it usually never stops at one obvious defect and old timers go into "overdrive" when they sense such."

    You need to be looking for the part which sank the Titanic - the part underwater you don't see.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11

    Default Re: Range hood vents to attached garage

    Forget the manufacturer specs, its an open penetration in a garage fire wall.

    Andrew Constantine
    InspectPro Home Inspections
    Charlotte NC Home Inspector


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •