    Erwin, TN
    Default Church Covered Patio Electrical
    IM sure this is wrong but I wanted to check with some experts. This 100 Amp secondary distribution panel in outside on a covered patio, its wired with grounds and neutral on the same bus bar, wrong or not ? Commercial wiring make a difference ?
    Default Re: Church Covered Patio Electrical
    It doesn't matter what type of building (i.e., church), or where it is mounted (i.e., covered porch), what matters is whether or not that is the "service equipment" for the structure.
    From what I see, there is almost no likelihood that is the service equipment for that church ... but only you can answer that question.
    If that is not the service equipment for that building, then the grounds and neutrals need to no be on the same terminal bar as the neutral needs to be isolated from ground at all locations after the service equipment.
    Chico,Ca
    Looks like a "good church member" install, and was too cheap, lazy, & ignorant, to buy a ground bar kit, not a place to be any of the three, at least they pulled all 4 conductors.
    What size were the feeder conductors? That is a single phase panel & there are 3 circuits with only a single neutral, missing a handle tie for the MWBC, the extra hot can lead to a burned neutral, pretty much a heavily flawed install.
    Oct 2014
    With no main bonding jumper or grounding electrode conductor
