Results 1 to 11 of 11
  1. #1
    wes owens's Avatar
    wes owens Guest

    Default non-tempered glass

    I think I'm correct about this but I wanted to double check before putting it in my report.

    The window is not tempered glass and as you can see, the door is less than 2ft. away.
    Now, my questions are, even though the door can't quite reach the glass because of the brick, the window should still be tempered, correct?

    Or does that apply only to situations where the door can actually come in contact with the window?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: non-tempered glass

    Wes,

    In my opinion, I think that you need safety glass in the door but not the adjacent window.

    This is from the 03 IRC:

    For the door:

    [b] R308.4 Hazardous locations.
    The following shall be considered specific hazardous locations for the purposes of glazing:
    1. Glazing in swinging doors except jalousies.
    For the adjacent window:

    6. Glazing, in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface.
    Exception: The following products, materials and uses are exempt from the above hazardous locations:
    3. Glazing in Section R308.4, Item 6, when there is an intervening wall or other permanent barrier between the door and the glazing.



  3. #3
    Join Date
    Mar 2007
    Location
    Garland, TX
    Posts
    652

    Default Re: non-tempered glass

    Try this

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by BARRY ADAIR; 04-17-2007 at 04:53 AM.
    badair http://www.adairinspection.com Garland, TX 75042
    Commercial-Residential-Construction-EIFS-Stucco-ACMV-Infrared Thermography
    life is the random lottery of events followed by numerous narrow escapes...accept the good

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: non-tempered glass

    Tim is close (but no seegar).

    From the IRC.
    - R308.4 Hazardous locations. The following shall be considered specific hazardous locations for the purposes of glazing:
    - - 6. Glazing, in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface. (Jerry's note: This *includes* that window.)
    - - Exception: The following products, materials and uses are exempt from the above hazardous locations: (Jerry's note: These Exceptions remove (except out) the following items from the above list, and there are exceptions to 6.)
    - - - 2. Decorative glass in Items 1, 6 or 7. (Jerry's note: This exception does not apply.)
    - - - 3. Glazing in Section R308.4, Item 6, when there is an intervening wall or other permanent barrier between the door and the glazing. (Jerry's note: This exception does not apply as there is no intervening wall or other permanent barrier.)
    - - - 4. Glazing in Section R308.4, Item 6, in walls perpendicular to the plane of the door in a closed position, other than the wall toward which the door swings when opened, or where access through the door is to a closet or storage area 3 feet (914 mm) or less in depth. Glazing in these applications shall comply with Section R308.4, Item 7. (Jerry's note: This exception does not apply as the exception itself excepts out from the exception "other than a wall toward which the door swings when opened, i.e., the wall where that window is. If not excepted out, then it remains in, meaning that that window *requires* safety glass as it is considered a hazardous location.)

    Clear as mud?



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: non-tempered glass

    Wes,

    I always explain it to my client as such. When the door is opened and if a person was standing behind that door could accidentally be struck by the door and fall backwards into a window, by all means that window should be safety glass.

    You put codes out if front of some people and it looks like Latin to them.

    Simple logic sometimes works best.

    Rick


  6. #6
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: non-tempered glass

    Kinda reads like Latin to me

    Not exacty sure on the code.

    I read it as the door needs to be safety glassed, but the wall window doesn't.


    Correct???

    If not, please explane in English. I only read foul


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: non-tempered glass

    I will try it again.

    From the IRC.
    - R308.4 Hazardous locations. The following shall be considered specific hazardous locations for the purposes of glazing:

    - - 6. Glazing, in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface.
    (Jerry's note: This *includes* that window.)

    - - Exception: The following products, materials and uses are exempt from the above hazardous locations:
    (Jerry's note: These Exceptions remove (except out) the following items from the above list, and there are exceptions to 6.)

    - - - 2. Decorative glass in Items 1, 6 or 7.
    (Jerry's note: This exception does not apply.)

    - - - 3. Glazing in Section R308.4, Item 6, when there is an intervening wall or other permanent barrier between the door and the glazing.
    (Jerry's note: This exception does not apply as there is no intervening wall or other permanent barrier.)

    - - - 4. Glazing in Section R308.4, Item 6, in walls perpendicular to the plane of the door in a closed position, other than the wall toward which the door swings when opened, or where access through the door is to a closet or storage area 3 feet (914 mm) or less in depth. Glazing in these applications shall comply with Section R308.4, Item 7.
    (Jerry's note: This exception does not apply as the exception itself excepts out from the exception "other than a wall toward which the door swings when opened, i.e., the wall where that window is. If not excepted out, then it remains in, meaning that that window *requires* safety glass as it is considered a hazardous location.)

    All I did was separate it so you could read it better.

    Did that help?

    Think of the exception to the exception this way: It's a double negative.

    Like saying: "I ain't got none", which means that you have some.

    If you except it out of the exception, it means you are leaving in the requirement.


    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: non-tempered glass

    Tim,

    Typically, windows within 24" of a door are required to be safety glass. A few years ago, this was modified from 12" (at least in the old UBC).

    That falls under Jerry's --6

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  9. #9
    wes owens's Avatar
    wes owens Guest

    Default Re: non-tempered glass

    Thanks guys.


  10. #10
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: non-tempered glass

    Thank you Jerry/Gunnar,

    The two areas that I was misreading was the 24" part here:

    where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position


    For some reason I was thinking that applied to the latch side of the door not the hinged side.

    Second one:

    when there is an intervening wall or other permanent barrier between the door and the glazing.
    I guess when I saw the brick under the window sticking out like that I was thinking that that was the permanent barrier between the door and the glazing.

    Thank you both for the clarification.



  11. #11
    Richard Rushing's Avatar
    Richard Rushing Guest

    Default Re: non-tempered glass

    Quote Originally Posted by Jerry Peck View Post
    I will try it again.

    From the IRC.
    - R308.4 Hazardous locations. The following shall be considered specific hazardous locations for the purposes of glazing:

    - - 6. Glazing, in an individual fixed or operable panel adjacent to a door where the nearest vertical edge is within a 24-inch (610 mm) arc of the door in a closed position and whose bottom edge is less than 60 inches (1524 mm) above the floor or walking surface.
    (Jerry's note: This *includes* that window.)

    - - Exception: The following products, materials and uses are exempt from the above hazardous locations:
    (Jerry's note: These Exceptions remove (except out) the following items from the above list, and there are exceptions to 6.)

    - - - 2. Decorative glass in Items 1, 6 or 7.
    (Jerry's note: This exception does not apply.)

    - - - 3. Glazing in Section R308.4, Item 6, when there is an intervening wall or other permanent barrier between the door and the glazing.
    (Jerry's note: This exception does not apply as there is no intervening wall or other permanent barrier.)


    - - - 4. Glazing in Section R308.4, Item 6, in walls perpendicular to the plane of the door in a closed position, other than the wall toward which the door swings when opened, or where access through the door is to a closet or storage area 3 feet (914 mm) or less in depth. Glazing in these applications shall comply with Section R308.4, Item 7.
    (Jerry's note: This exception does not apply as the exception itself excepts out from the exception "other than a wall toward which the door swings when opened, i.e., the wall where that window is. If not excepted out, then it remains in, meaning that that window *requires* safety glass as it is considered a hazardous location.)

    All I did was separate it so you could read it better.

    Did that help?

    Think of the exception to the exception this way: It's a double negative.

    Like saying: "I ain't got none", which means that you have some.

    If you except it out of the exception, it means you are leaving in the requirement.
    Illustration--

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •