Results 1 to 13 of 13
  1. #1
    wes owens's Avatar
    wes owens Guest

    Default vertical pipe on relief line

    This pressure relief line is vertical for 13" before going through the wall.
    I wanted to see what you guys thought.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Oct 2003
    Location
    Rockwall Texas
    Posts
    4,521

    Default Re: vertical pipe on relief line

    Wes,

    The T&P drain line can't run in an upwards position regardless.

    And that electrical supply line should be enclosed in protective material.

    Rick


  3. #3
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: vertical pipe on relief line

    Wes, as you most likely know, that PTR line should terminate straight down or to the exterior assuming that is slopes down as Rick stated.

    Also is that pipe PVC or CPVC? PVC is not allowed for that application.

    From the 03 IRC:

    P2803.6.1 Requirements of discharge pipe.
    The outlet of a pressure relief valve, temperature relief valve or combination thereof, shall not be directly connected to the drainage system. The discharge from the relief valve shall be piped full size separately to the floor, to the outside of the building or to an indirect waste receptor located inside the building. In areas subject to freezing, the relief valve shall discharge through an air gap into an indirect waste receptor located within a heated space, or by other approved means. The discharge shall be installed in a manner that does not cause personal injury or property damage and that is readily observable by the building occupants. The discharge from a relief valve shall not be trapped. The diameter of the discharge piping shall not be less than the diameter of the relief valve outlet. The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches (152 mm) above the floor. The outlet end of the discharge pipe shall not have a valve installed.


  4. #4
    wes owens's Avatar
    wes owens Guest

    Default Re: vertical pipe on relief line

    It is CPVC.


  5. #5
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: vertical pipe on relief line

    I'm sure someone else knows for sure, but I thought no plastic pipe to the water heater for the last 18".

    Jim Robinson
    New Mexico, USA

  6. #6
    Brian E Kelly's Avatar
    Brian E Kelly Guest

    Default Re: vertical pipe on relief line

    There are plastic relief valve tubes sold and approved by local code inspectors. At least here in BOONIES NY. This pipe is actually a thinner pipe that CPVC or PVC pipe. Go figure.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: vertical pipe on relief line

    Quote Originally Posted by Rick Hurst View Post
    The T&P drain line can't run in an upwards position regardless.
    Well, I hate to dispute you, but ... ... "it can", you were looking at it.

    I know, you meant to say that it "should not" or "is not allowed to".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: vertical pipe on relief line

    Quote Originally Posted by Jim Robinson View Post
    I'm sure someone else knows for sure, but I thought no plastic pipe to the water heater for the last 18".
    CPVC is approved for use as T&P relief valve discharge lines.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  9. #9
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: vertical pipe on relief line

    Quote Originally Posted by Jim Robinson View Post
    I'm sure someone else knows for sure, but I thought no plastic pipe to the water heater for the last 18".
    Jim - Maybe you're thinking of the hot/cold connections at the top. I believe cpvc should not be used within 18" of those.

    "There is no exception to the rule that every rule has an exception." -James Thurber, writer and cartoonist (1894-1961)
    www.ArnoldHomeInspections.com

  10. #10
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: vertical pipe on relief line

    Yes. I had no problem with the CPVC for the TPR. I was referring to the incoming cold and outgoing hot water lines on top of the water heater.

    Jim Robinson
    New Mexico, USA

  11. #11
    Tim Moreira's Avatar
    Tim Moreira Guest

    Default Re: vertical pipe on relief line

    Without looking it up, I thought CPVC was permitted for distribution piping?

    Yes or No???


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: vertical pipe on relief line

    The only problem with the CPVC for the hot or cold would be if that was not electric, but it is.

    The CPVC would, should, be 6" from the draft hood.

    Even poly bute was only 12" from a heat source like the draft hood.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: vertical pipe on relief line

    My bad. I didn't realize it was electric. I rarely see an electric water heater (five or six times a year) so I didn't even think about that aspect.

    Jim Robinson
    New Mexico, USA

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •