    this is a sub-panel and has the copper bond attaching the cabinet to the neutral bar. Seems to be the same problem as with grounds and neutrals? The grounding i believe is in the raceway/conduit. no ground wires were present in the cabinet.

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: sub panel bonded with neutrals

    No pic Jerome.


  3. #3
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default Re: sub panel bonded with neutrals

    sorry I though i had one but i didnt. The copper jumper was just connected from the neutral bar to the sub panel cabinet. metal raceways were used to protect the circuits. i didnt know if that changed the rules on bonding grounds and neutrals etc.


  4. #4
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: sub panel bonded with neutrals

    The metal raceways themselves should be bonded to ground. With the neutral and grounds bonded in that non-service equipment panel, now you have neutral current on the raceways. Neutrals and grounds should only be bonded at the service equipment. Jerry Peck may have some comment regarding submarines...


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: sub panel bonded with neutrals

    Quote Originally Posted by John Arnold View Post
    Jerry Peck may have some comment regarding submarines...
    I was going to ask Jerome if he had a photo of the sub that panel was in, but he said he had no photo. I keep hoping to see a real "sub" panel.

    Neutrals and grounds should only be bonded at the service equipment.
    Correct. Meaning that "bonding jumper" should not go from the neutral terminal bar to the enclosure *at any panel which is not service equipment*.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Jerome W. Young's Avatar
    Jerome W. Young Guest

    Default Re: sub panel bonded with neutrals

    , that's damn funny

    Thanks!


Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •