    Default how many neutral wires

    hey can anyone tell me what the nec says about how many neutral wires you can jam into a buse screw

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: how many neutral wires

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Western Montana
    Posts
    261

    Default Re: how many neutral wires

    The State electrical inspector in my area has ignored that code for the past 15 or so years; he has always approved panels that may have 2 or 3 neutrals on the same terminal, or mixing neutrals and grounding conductors on the same terminal. I believe one of the first sections in the NEC has some clause that the local jurisdiction enforcer can supercede code (so I've been told). Now however that he has retired, I pity his replacement that has to re-train all the electricians in the area.


  4. #4
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: how many neutral wires

    this house was built in 1974----how would you write it up--code didn't apply back then--recommend licenced electrician evaluate


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: how many neutral wires

    Two conductors are NEVER allowed in the same terminal ... unless the terminal is listed and labeled for such.

    Thus, unless you read on the instruction sheet where it tells what terminal is for what, etc., and it SPECIFICALLY stated 'neutral terminals suitable for 2 - 14 AWG to 10 AWG or something to that effect, that practice was not allowed back then either.

    Later, to end the confusion, the code and UL both said 'no, never' to that.

    Now, *IF* (that big "if) the manufacturer states on their label that it as suitable for that use, then, yeah, not much you can do about it other than advise your client 'In the intervening years, much as been learned about electricity and wiring, including installing two neutral conductors in one terminal, and all that learned knowledge and experience says *THAT IS NOT A GOOD THING* to do, so it NEEDS TO BE corrected anyway.'

    Being as you likely did not find anything saying it was suitable for that use, it was, therefore, NOT suitable for that use.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: how many neutral wires

    saw nothing thanks jerry


  7. #7
    Join Date
    Mar 2009
    Location
    NY
    Posts
    5

    Default Re: how many neutral wires

    Charlie ..Did you used to work for AT&T?


  8. #8
    Michael Larson's Avatar
    Michael Larson Guest

    Default Re: how many neutral wires

    NEC 408.41 Each grounded conductor shall terminate within a panel board in an individual terminal that is not used for any other conductor


  9. #9
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: how many neutral wires

    hey jeff

    how ya doing yes i did

    email me at cvanfleet56@aol.com

    charlie