Results 1 to 13 of 13
  1. #1
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default De-rating Revisited

    Would you say that this bundle should be de-rated and/or appropriate repairs be conducted by a licensed and qualified electrician?
    I already called out the missing knockout.


    And, while I'm at it.... there was an addition to this house... a patio was enclosed.... some electrical was run.... all other breakers being original.... all squareD.... this one caught my eye.... could it be one of those bogus SquareD breakers?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Victor DaGraca; 03-15-2008 at 12:19 PM. Reason: after thought
    Inspection Referral
    Critical Home Inspection Services
    www.Home2Spec.com

  2. #2
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: De-rating Revisited

    Quote Originally Posted by Victor DaGraca View Post
    Would you say that this bundle should be de-rated and/or appropriate repairs be conducted by a licensed and qualified electrician?
    I already called out the missing knockout.
    Everything shouldn't be stuffed through together like that, but for de-rating they have to be bundled for at least 24 inches, if memory serves.


  3. #3
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: De-rating Revisited

    Thanks John.... now that you mentioned the 24"......

    Critical Home Inspection Services
    www.Home2Spec.com

  4. #4
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: De-rating Revisited

    I think that you will also find that strain relief clamps are required, not a bushing.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  5. #5
    David Banks's Avatar
    David Banks Guest

  6. #6
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: De-rating Revisited

    David;
    Here's the problem I'm having....

    your link shows a genuine breaker .... Connecticut Electric Recalls Counterfeit Square D Circuit Breakers Due To Fire Hazard

    this link shows a counterfeit.....
    Counterfeit "Square D" Circuit Breakers

    They look Identical

    The best comparison I got was at North American Breaker Co. Recalls Counterfeit Circuit Breakers Due to Fire Hazard

    Now.... look again at the picture I posted.... They look nothing like the genuine OR the counterfeit....

    I e-mailed Schneider electric hoping to get an answer...


    here's a pic of the comparison

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Critical Home Inspection Services
    www.Home2Spec.com

  7. #7
    David Banks's Avatar
    David Banks Guest

    Default Re: De-rating Revisited

    Quote Originally Posted by Victor DaGraca View Post
    David;
    Here's the problem I'm having....

    your link shows a genuine breaker .... Connecticut Electric Recalls Counterfeit Square D Circuit Breakers Due To Fire Hazard

    this link shows a counterfeit.....
    Counterfeit "Square D" Circuit Breakers

    They look Identical

    The best comparison I got was at North American Breaker Co. Recalls Counterfeit Circuit Breakers Due to Fire Hazard

    Now.... look again at the picture I posted.... They look nothing like the genuine OR the counterfeit....

    I e-mailed Schneider electric hoping to get an answer...


    here's a pic of the comparison
    I had the same problem looking at your pics. Thats why I posted the link with no comment. Good luck.


  8. #8
    Lee Nettnin's Avatar
    Lee Nettnin Guest

    Default Re: De-rating Revisited

    Victor,
    I believe your breaker is one of Square D's new Homeline series and is made to fit other panel boxes as well as there own.
    Lee


  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: De-rating Revisited

    Quote Originally Posted by Gunnar Alquist View Post
    I think that you will also find that strain relief clamps are required, not a bushing.
    Yep.

    So, even if they are like that for less than 24" ... they are *STILL* "wrong".

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: De-rating Revisited

    Jerry;
    Even though I can't ascertain that those wires do or don't run like that for 24" I'd still "assume" (dangerous word there) that the amount of wires and their proximity within that orifice would produce excessive heat build up.

    Of course I'm not an electrician or an engineer and even the IRC does not specifically dis-allow (prohibit) that specific scenario, that being said.... if it looks like a duck......

    Critical Home Inspection Services
    www.Home2Spec.com

  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,039

    Default Re: De-rating Revisited

    Quote Originally Posted by Victor DaGraca View Post
    Even though I can't ascertain that those wires do or don't run like that for 24"
    That's why I quoted Gunnar (and am doing so again).

    Quote Originally Posted by Gunnar Alquist View Post
    I think that you will also find that strain relief clamps are required, not a bushing.
    Forget about the 24" and derating, go on to something which is plainly visible.

    Correct THAT, and, by virtue of correcting that, you are also correcting the un-verifiable 24" ... whether or not if it - er - "was" (as in "past tense") 24" or greater, or less, no longer matters.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  12. #12
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: De-rating Revisited

    You know..... sometimes things in plain sight make a dope outa me.... All along I thought Gunnar was refering to the lone wire on the left coming through the bushing. (no strain relief clamp)
    THEN.... Outa the blue.......

    Thanks Jerry
    Thanks Gunnar
    Thanks to all...

    Critical Home Inspection Services
    www.Home2Spec.com

  13. #13
    Join Date
    Mar 2007
    Location
    Myrtle Beach, South Carolina
    Posts
    341

    Default Re: De-rating Revisited

    Ok... I received a reply from Schneider Electric. Here it is.
    Lee .... Looks like you hit it.

    Dear Victor DaGraca:
    Thank you for your internet inquiry. I asked the plant and corporate offices to look at this picture. Neither can confirm or deny that the breaker shown on that picture is a counterfeit breaker. From the corporate people, they have said there have been no known instances at this time of counterfeit HOM, or Homeline breakers.

    To verify for sure, we would need to have the product returned to us for inspection by one of our engineers. You may contact a local field sales office to initiate this process.

    To find the Square D/Schneider Electric Sales Office nearest you, click the following link:
    http://ecatalog.squared.com/ssearch/

    Please feel free to contact us, should you have any further questions.

    Regards,
    Kevin McDonald.
    Product Support Specialist.
    Schneider Electric
    1-888-778-2733

    Critical Home Inspection Services
    www.Home2Spec.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •