    I came across a 175 PSI TPR valve (instead of the usual 150 PSI). I've never seen one before. Where could you use it?

    Similar Threads:
    OREP Insurance
    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: 175 TPR valve

    Commercial boilers?

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: 175 TPR valve

    Thanks Jim

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  4. #4
    B Chapin's Avatar
    B Chapin Guest

    Default Re: 175 TPR valve

    Can use it anywhere. Tanks are rated to 300 psi, right?


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 175 TPR valve

    Quote Originally Posted by B Chapin View Post
    Can use it anywhere. Tanks are rated to 300 psi, right?
    Nope.

    P2803.3 Pressure relief valves.
    Pressure-relief valves shall have a relief rating adequate to meet the pressure conditions for the appliances or equipment protected. In tanks, they shall be installed directly into a tank tapping or in a water line close to the tank. They shall be set to open at least 25 psi (172 kPa) above the system pressure but not over 150 psi (1034 kPa). The relief-valve setting shall not exceed the tanks rated working pressure.



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired