    Default Clearance question

    I found this for the first time and seem to remember that there was a code dealing with this situation. Anyone have it handy? The pics not that great but it is a gas line in behind the condensing unit. It was built this way in 1994 and did have final inspection stickers. I just seem to remember this being an issue.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Last edited by Frank Bombardiere; 03-21-2008 at 02:10 PM. Reason: add discription of pic
    OREP Insurance
    If it weren't for lawyers, we would never need them.

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Clearance question

    The gas line can be there, but there needs to be at least (by most manufacturers) 12" between the condenser unit and the wall.

    Now, if there was a regulator there, that would be a different matter.

    Also, which side of the condenser unit has the access to the service area? That side requires 36" working space.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Oklahoma City
    Posts
    357

    Default Re: Clearance question

    Thanks Jerry, I couldn't really think of many reasons why it would not be allowed there, but thought I remembered something on another thread.

    If it weren't for lawyers, we would never need them.