    Hello to all,

    I have a question regarding the re-lining of a 6" Type-B furnace flue stack that now only serves an orphaned water heater.

    I am getting conflicting information about whether the 3" liner has to be Type-B pipe or not.

    Which is it, and why?

    Thanks.

    Similar Threads:
    OREP Insurance

  2. #2
    Jon Randolph's Avatar
    Jon Randolph Guest

    Default Re: Orphaned Water Heater Flue Requirements

    Don't quote me on this, other will likely be along shortly.

    I the vent goes un-protected through an unconditioned space, such as an attic, it needs to be class b. If it will go entirely through an old chimney chase, single wall.


  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: Orphaned Water Heater Flue Requirements

    The flue can be up to 7x the size of the smallest appliance. However, it will perform like a dog. It should be re-vented using B-vent installed to the listed instructions. If it vents into a chimney, it should be relined sized to the WH. It isn't up to the H.I. to specify the liner size, only it needs to be sized to fit that appliance and let the pros size it, whether B-vent or liner.

    Single walled vent connector not allowed in unconditioned spaces or as chimney liner. Listed liner only.

    HTH,
    Bob

    Keep the fire in the fireplace.