Results 1 to 10 of 10

Thread: Flue clearance

  1. #1
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Flue clearance

    Does a water heater flue pipe require the same 3-2-10 rule same as firplaces. For the life of me I cant find my reference.

    Jim

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    David Banks's Avatar
    David Banks Guest

    Default Re: Flue clearance

    Do not have code but if closer than 8 feet to wall vent must extend 2 feet above roof.


  3. #3
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Flue clearance

    Jim, I'm not sure about that. But how close is that flue pipe to the adjacent roof surface? Is that type-B vent or single walled?


  4. #4
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Re: Flue clearance

    That's single walled pipe. The pipe is almost touching the wood fascia. I have the one inch clearance from the roof sheathing but I dontThink I have one inch from the fascia. I'm also concerned about drafting properly.

    Jim


  5. #5
    David Banks's Avatar
    David Banks Guest

    Default Re: Flue clearance

    NFPA 54 12.7.2. Gas Vent Terminations.
    A.........
    B Gas vents that are over 12 inches in size or are located less than 8 ft. from a vertical wall or similar obstruction shall terminate not less than 2 ft. above the highest point where they pass through the roof and not less than 2 ft. above any portion of a building within 10 ft horizontally.


  6. #6
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Re: Flue clearance

    Thanks david,
    This site Rocks when I need it.


  7. #7
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flue clearance

    Quote Originally Posted by James Bohac View Post
    That's single walled pipe. The pipe is almost touching the wood fascia. I have the one inch clearance from the roof sheathing but I dontThink I have one inch from the fascia. I'm also concerned about drafting properly.

    Jim
    Single Walled pipe clearance is 6 inches. B vent is 1 inch clearance from combustibles.

    Quote Originally Posted by David Banks View Post
    NFPA 54 12.7.2. Gas Vent Terminations.
    A.........
    B Gas vents that are over 12 inches in size or are located less than 8 ft. from a vertical wall or similar obstruction shall terminate not less than 2 ft. above the highest point where they pass through the roof and not less than 2 ft. above any portion of a building within 10 ft horizontally.
    Also IRC. 2003 M1804.2.6

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  8. #8
    David Banks's Avatar
    David Banks Guest

    Default Re: Flue clearance

    Quote Originally Posted by James Bohac View Post
    That's single walled pipe. The pipe is almost touching the wood fascia. I have the one inch clearance from the roof sheathing but I dontThink I have one inch from the fascia. I'm also concerned about drafting properly.

    Jim
    That single wall should not be going through the attic. Needs to be type B or L.


  9. #9
    Join Date
    Mar 2007
    Location
    Baton Rouge, La.
    Posts
    91

    Default Re: Flue clearance

    My bad, That is a type B flue, however it is less than 12 inches in diameter. Does the same clearance from horizontal objects apply?

    Jim


  10. #10
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Flue clearance

    Quote Originally Posted by James Bohac View Post
    My bad, That is a type B flue, however it is less than 12 inches in diameter. Does the same clearance from horizontal objects apply?

    Jim
    Yes..

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.