    Default spa pump pressure switch in panel

    I guess this is called a presssure switch. It activated the spa jet pump when i depressed the air switch. I am fairly confident it should not be inside this panel, but why?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: spa pump pressure switch in panel

    "I am fairly confident it should not be inside this panel, but why?"

    Mainly because the panel is not listed for being used as an enclosure for that contactor (or things like that it).

    I also see (as I am sure you did) multiple tapped neutral, multiple tapped breaker and feeders which are likely too small for the terminals they are in.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com