Results 1 to 4 of 4
  1. #1
    Wendell Swedberg's Avatar
    Wendell Swedberg Guest

    Default Maximum fill for conductors in a panel board

    Okay, today's test question:

    The maximum fill permitted for conductors, excluding splices and taps, in a panelboard is limited to what maximum percent?

    a) 10
    b) 20
    c) 40
    d) 75

    Answer is (C)-40......I can't find out how this is being derived.

    Thanks.

    Wen

    Similar Threads:
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Maximum fill for conductors in a panel board

    From the 2006 IRC. (underlining is mine)
    - SECTION E3807
    - - CABINETS AND PANELBOARDS
    - - - E3807.1 Enclosures for switches or overcurrent devices.
    Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, except where adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    Healdsburg, CA
    Posts
    1,741

    Default Re: Maximum fill for conductors in a panel board

    So Jer, you would consider this overfill according to the code?

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Jerry McCarthy
    Building Code/ Construction Consultant

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Maximum fill for conductors in a panel board

    WC Jerry,

    Nah, I see some splices in there, so that can go to 75% ... that's not over 75% is it?

    (Way over 75%. )

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •