    Default CSST through exterior wall?

    Seems I remember a discussion about CSST not being allowed through an exterior wall.

    Rumaged through Code Check but did not find anything.

    Any hints or it is OK?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    "The Code is not a peak to reach but a foundation to build from."

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: CSST through exterior wall?

    From the Wardflex site.

    l
    WARDFLEX Mechanical Joint Fittings shall be protected from the effects of weather when used out
    doors. After the connection is made to outdoor equipment the WARDFLEX Mechanical Joint Fitting
    shall be sealed by wrapping two layers of tape (e.g. PVC, Silicone) or by applying shrink sleeves (e.g.
    PVC, Polyolefin).
    l


    The following additional instructions regard the use of WARDFLEX in systems in which portions of the
    piping are exposed to the outdoors as required to make connections to gas meters or gas appliances,
    which are attached to, mounted on, or located in close proximity to the building structure.
    l


    In cases where conflicting requirements exist, the order of precedence shall be as follows:
    1 - Local Code
    2 - Manufacturer’s Instructions
    l


    The external protective covering shall remain intact as much as practical for the given installation.
    l


    When installed along the side of a structure (between the ground and 6 ft.) in an exposed condition, the
    WARDFLEX must be protected inside a conduit or installed in a location which will not subject it to
    mechanical damage.


    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Atlanta, Georgia
    Posts
    1,088

    Default Re: CSST through exterior wall?

    Thank you for the quick response. Wow! The diagram is exactly what I saw today.

    "The Code is not a peak to reach but a foundation to build from."

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: CSST through exterior wall?

    Quote Originally Posted by Bruce Ramsey View Post
    Wow! The diagram is exactly what I saw today.

    Bruce,

    Actually, your photo appears (not having been there, only looking at the photo) to be missing a critical part in that drawing.

    Those meters are designed to be supported from both sides, and CSST is not allowed to support a meter.

    In your photo, the meter is leaning down on the right, from lack of support.

    Now, going back to figure 4.14, you will note, in all three drawings, that the meter is supported independently of the CSST.

    Thus, the installation in your photo is incorrect ... the meter requires an additional support.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default Re: CSST through exterior wall?

    And the meter should not be sitting in the dirt!