Thread: Steam generator

  1. #1
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Steam generator

    Is this a valid connection for a steam generator tpr discharge line?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Spring City/Surrounding Philadelphia area
    Posts
    3,509

    Default Re: Steam generator

    Hmmm. Exhaust tube goes uphill. Not sure what the manufacturer calls for but my first inclination would be NG..........as in No Good. I know some areas require these exhaust tubes to be plumbed differently but I don't like the idea of sending a TPR tube directly into a drain line as you will not know if the valve is opening which could indicate a defect with the unit it serves.

    Also, is that a polybutylene supply line I see in those pics?


  3. #3
    mathew stouffer's Avatar
    mathew stouffer Guest

    Default Re: Steam generator

    Nick,
    Good points. It is not polybutylene. I was curious if a gap is required, although your point about not being able to identify if the tpr has failed is a good point. The whole set up is a mess because it is missing a drain pan which is required in this area. Thanks for the info.

    Mat


  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Steam generator

    Forget NG, go with NFG ...

    First, it goes uphill - that part's NG.

    Second, if that thing discharges, it will blow that trap apart, and that is not an approved connection (there should be no connection) - that part's NFG.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Steam generator

    Hell no, let's see...
    - essentially double trapped
    - connected with a hose
    - connected to a plastic sink trap, which as Jerry stated most likely won't handle the pressure
    - then of course there's the temperature issue, imagine how hot (+/- 180 degrees) that water is going to be
    - since that release is going to be under a lot of pressure it is unlikely it will confine itself to going down the drain; I wouldn't be at all surprised to see a geyser shoot up out of the sink

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  6. #6
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Steam generator

    also the unsecured 1900 box laying there
    and what are those loose black and white wires in the background by the wall?

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"