Results 1 to 9 of 9
  1. #1
    Join Date
    Jul 2007
    Location
    Chicago
    Posts
    187

    Default Stucco clearance from roof

    This home has approx 30" overhang but this appears wrong even if there is step flashing buried. Doesn't ALL siding require 2" space?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Stucco clearance from roof

    Unless it is stucco on block (and that is likely stucco on frame) ... stucco on frame is a drainage system and requires space to drain. While 2" comes to my mind, it could be more or less than that, however, I would go with 2" until proven wrong (or until I looked it up) as that would provide the drainage space for the wall/weep flashing to drain/weep up.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Aug 2007
    Location
    Bethlehem,Pa.
    Posts
    35

    Default Re: Stucco clearance from roof

    No termination bead or caulking at the window either.


  4. #4
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: Stucco clearance from roof

    It is 2" off the surface of the roof.

    Another reason for the distance is so that the roof can be replaced as needed without damaging the stucco.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  5. #5

    Default Re: Stucco clearance from roof

    Doesn't ALL siding require 2" space
    A min. of 1" clearance is required for other siding types.


  6. #6
    RobertSmith's Avatar
    RobertSmith Guest

    Default Re: Stucco clearance from roof

    Quote Originally Posted by Brandon Whitmore View Post
    A min. of 1" clearance is required for other siding types.
    Could someone please cite the source for clearance...I've looked in the 2006 code book, I can't find it. Nor can I find it in manufacturer installation instructions.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,036

    Default Re: Stucco clearance from roof

    Quote Originally Posted by RobertSmith View Post
    Could someone please cite the source for clearance...

    Robert,

    It's in the ASTM standard, C 1063, Standard Specification for Installation of Lathing and Furring to Receive Interior and Exterior Portland Cement-Based Plaster
    (Note, while we are not referencing "foundation" weep screed, we are referencing "weep screed", which, like "foundation" "weep screed" must be allowed to have room to ... well, "weep".) (underlining is mine)
    - 7.11.5 Foundation Weep Screed — Foundation weep screed shall be installed at the bottom of all steel or wood framed exterior walls to receive lath and plaster. Place the bottom edge of the foundation weep screed not less than 1 in. (25 mm) below the joint formed by the foundation and framing. The nose of the screed shall be placed not less than 4 in. (102 mm) above raw earth or 2 in. (51 mm) above paved surfaces. The weather resistive barrier and lath shall entirely cover the vertical attachment flange and terminate at the top edge of the nose or ground flange.

    Treat that weep screed (which is missing) as "foundation weep screed" (it serves that same purpose), and treat the roof as "paved surfaces" (the roof serves that same purpose).



    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Tampa, Fl
    Posts
    155

    Default Re: Stucco clearance from roof

    Northwest Wall and Ceiling Bureau says you need 2"


  9. #9

    Default Re: Stucco clearance from roof

    Could someone please cite the source for clearance...I've looked in the 2006 code book, I can't find it. Nor can I find it in manufacturer installation instructions.
    Without looking into the codes, I can tell you that James Hardie products requires a 1-2" min. clearance under 4,000 feet, and a min. 2" clearance above 4,000 feet (Western US instructions).

    I can't tell you where else I have seen the requirements over the years. Hardie Plank is so often used around here I pretty much know their instructions by heart.

    Last edited by Brandon Whitmore; 05-19-2008 at 10:14 PM. Reason: Forgot Quote

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •