    Default Furnace in kitchen & Return air from outside

    Inspection yesterday.

    - LP Gas: Furnace and water heater located in the kitchen. (had electric range)

    - There were no Hi/Low combustion air vents installed.

    - The cold air return was exterior grill / vent (outside air). There was no return air duct system installed returning interior air

    - Can "all" of return air come from outside? Seems as though house would be pressurized??

    - Living room was only room with heated air ductwork (crawl area).... wood stove in living room.

    - Kitchen had no heated air ductwork (slab construction).

    - Separate area had direct vent LP gas wall furnace.

    By the way the living room area was a mobile home 10' x 55' with framed envelope built around it!!!! very strange!!!

    Pictures show metal siding... metal frame and wheel hubs in crawl area!!

    Electrical: Service entry wire (cable) from meter to SEC panel was exposed above ground

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper
    Charles @ PreVue Property Inspections, Santa Fe, NM
    http://www.prevuepropertyinspections.com/
    "How can someone with glasses so thick be so stupid?"

  2. #2
    Randy Clayton's Avatar
    Randy Clayton Guest

    Default Re: Furnace in kitchen & Return air from outside

    Charles, I don't deal with mobile homes but onne thing I did see is that where the furnace and wh exaust came together the size of the flue did not increase in size.


  3. #3
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Furnace in kitchen & Return air from outside

    Can "all" of return air come from outside? Seems as though house would be pressurized??
    Prohibited in the IRC.

    From the sound of it this is truly a "bubba built" POS.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  4. #4
    Join Date
    Mar 2007
    Location
    Santa Fe, NM
    Posts
    74

    Default Re: Furnace in kitchen & Return air from outside

    Yes, the furnace and WH exhaust vent had no Wye connector and the size was not increased to accomodate both gas appliances.

    Trying to find the specific IRC reference on % of outside air brought into return and ran across...

    "If the outside air duct is connected directly to the return air trunk line, the connection must be a minimum of five feet from the furnace blower. The outside air cfm cannot exceed 10% of furnace flow."

    Any other input would be appreciated.

    Thanks

    Charles @ PreVue Property Inspections, Santa Fe, NM
    http://www.prevuepropertyinspections.com/
    "How can someone with glasses so thick be so stupid?"

  5. #5
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Furnace in kitchen & Return air from outside

    Can "all" of return air come from outside?
    2003 IRC Section M1602 Return Air
    M1602.1 Return air. Return air shall be taken from inside the dwelling. Dilution or return air with outdoor air shall not be prohibited.

    The idea is that the system should be balanced so that the return air and the supply air to the dwelling should be roughly equal. If there is a return strictly from outdoors, it is wrong, no calculation needed. Otherwise, see M1602.2 in the IRC to start with if you are under the IRC.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  6. #6
    Join Date
    Mar 2007
    Location
    Succasunna NJ
    Posts
    577

    Default Re: Furnace in kitchen & Return air from outside

    If the furnace was fan assisted venting, the WH vent may have been increased to accomadate the fan and there would be no need to increase the the vent after the connection.

    Darren www.aboutthehouseinspections.com
    'Whizzing & pasting & pooting through the day (Ronnie helping Kenny helping burn his poots away!) (FZ)

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •