Results 1 to 11 of 11
  1. #1
    imported_John Smith's Avatar
    imported_John Smith Guest

    Default Electrical under kitchen island

    The receptacle box doesnt seem to be correct for this type of application (receptacle in side of cabinet under island counter). I thought they were only for recessed applications into walls.

    In addition, the metal box and wiring to the receptacle seem to be a lazy way of running power from under the cabinet to the receptacle. They sure take up a lot of space in the cabinet. Thoughts?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Electrical under kitchen island

    At least they protected the wire. It should be secured though. I see similar in center island cabinets. The boxes are secured. Yes, it does

    Ted


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Electrical under kitchen island

    The installation of that box in a cabinet is not a problem.

    MAKING A HOLE THAT LARGE THROUGH THE SIDE it, though. Those boxes are designed to have the NM cable enter through the built-in clamps, in the corners, there is no way there is sufficient wire bending space, much less space for the lock nut on the inside, between the end of that fitting and the device (receptacle)!

    That's a mulligan. (Do it over. For free. )

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    imported_John Smith's Avatar
    imported_John Smith Guest

    Default Re: Electrical under kitchen island

    Thanks guys. It seems to be like the knockout tab near the top being open would be a problem. I dont know why, but I thought that the blue plastic boxes were only allowed to be recessed in a wall.


  5. #5
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Electrical under kitchen island

    John,

    They are available for "new work" and "old work" with the difference being in the way they are mounted.

    "New work" is attached to the stud, nails, screws, etc.

    "Old work" is secured to the wall surface (gypsum board, wood, etc.) with clamps of various means and methods.

    When mounted in wood, the front edge of that box is required to be even with, or extend out beyond, the combustible surface ... not allowed to be recessed back 1/4" as if in a gypsum board wall.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  6. #6
    imported_John Smith's Avatar
    imported_John Smith Guest

    Default Re: Electrical under kitchen island

    Thanks Jerry.


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Electrical under kitchen island

    John,

    just because the box is allowed does not mean they are allowed to mutilate it like that.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: Electrical under kitchen island

    Why would the guy use liquidtight, a metal 1900 box and a plastic box for that install? He must have watched on of the DIY shows.
    Curious, did you test the recep for grounding. I kind of doubt it is legitimately grounded.

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  9. #9
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Electrical under kitchen island

    Quote Originally Posted by Markus Keller View Post
    Curious, did you test the recep for grounding. I kind of doubt it is legitimately grounded.
    Markus,

    I hope it is grounded, probably won't take much to short/ground fault out those pinched-between-the-box-side-and-receptacle-screws conductors.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  10. #10
    Shannon Guinn's Avatar
    Shannon Guinn Guest

    Default Re: Electrical under kitchen island

    Plus, I hope that ENT was secured in place.


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,038

    Default Re: Electrical under kitchen island

    Quote Originally Posted by Shannon Guinn View Post
    Plus, I hope that ENT was secured in place.
    Yeah, and the photos are of a small enough view that the 12" from the box is not visible.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •