    Default Condensor Clearance

    I cannot find the installation instructions for this Armstrong Concept 1000 compressor. Is there a general rule of thumb for clearance to the wall? It was about 3 inches away , and seemed too close to me.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Member Benefits1
    Jim Robinson
    New Mexico, USA

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Condenser Clearance

    Quote Originally Posted by Jim Robinson View Post
    Is there a general rule of thumb for clearance to the wall?
    Generally, 12" is the least clearance allowed, plus, not under roof water runoff.

    Also, if the service access faces the wall, then 36" is required between the unit and the wall (to meet the minimum working space requirements).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2007
    Location
    New Mexico
    Posts
    1,352

    Default Re: Condensor Clearance

    Dang, that was quick. Thank you, as always.

    Jim Robinson
    New Mexico, USA

  4. #4
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Condensor Clearance

    You can ask them here http://www.armstrongair.com/contact.php, or call Lennox, 1-800-953-6669. That's the "customer care" number, but I've been able to get tech support numbers there in the past by explaining why I'm asking.

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  5. #5

    Default Re: Condensor Clearance

    The one I had yesterday required 8"-- that's the least I have seen.