    Other than sloppy workmanship is there any reason why a HVAC installer would just leave the zoning panel and transformer just laying on top the attic equipment like this? I've probably done over 3000 inspections and never seen crap like this on a brand new install. I don't know of any building codes that would prohibit it other than the general manufacturers installation manual.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Mar 2007
    Location
    Columbus GA
    Posts
    3,747

    Default Re: HVAC New Installation

    If the transformer has live wires connected to it then it should be mounted in an enclosure.
    As for the zoning panel ? Don't know. Maybe the instructions say where/ how and if, it should be mounted to anything.
    PS
    Alarm equipment should not be located in the attic because the temperature can exceed manufactures limits.
    This may apply the other electronic equipment as well.

    ' correct a wise man and you gain a friend... correct a fool and he'll bloody your nose'.

  3. #3
    Join Date
    May 2007
    Location
    Frankfort, KY
    Posts
    326

    Default Re: HVAC New Installation

    If you can get your hands on the install instructions for that zone panel I would bet it isn't approved for installation in an attic like that.

    Transformer should have been mounted in the equipment with the line voltage wiring NOT exposed like it is.

    I've seen a lot of bad zone systems but yours has to take the prize Ken.

    Measured Performance more than just a buzzword

  4. #4
    Join Date
    Feb 2008
    Location
    Chicago IL
    Posts
    2,048

    Default Re: HVAC New Installation

    - Transformer should be screwed on inside the cabinet with the rest of the controls.
    - We don't allow romex at all, so I'm guessing nonetheless it shouldn't be hanging in the air like that.
    - Is that a yellow flex gas hose to the unit instead of black pipe?
    - panel should be mounted somewhere

    www.aic-chicago.com
    773/844-4AIC
    "The Code is not a ceiling to reach but a floor to work up from"

  5. #5
    Randy Clayton's Avatar
    Randy Clayton Guest

    Default Re: HVAC New Installation

    Just plain poor quality install.


  6. #6
    Join Date
    Aug 2008
    Location
    Pleasant Hill, Iowa
    Posts
    145

    Default Re: HVAC New Installation

    Zone Control panel needs to be mounted!
    This is a 40 VA transformer and the line voltage wires (BLK & White) go inside of the unit.The unused orange wire appears to be for a 240 Volt primary use. The transformer should have been mounted and secured with the line voltage wires in a box. The control wires can be outside the unit. The transformer can also be mounted outside the unit so long as it is secured. They used the wrong style of transformer, They should have used a box mount 40 VA transformer and installed another box on top of this unit. Just poor workmanship !

    Dan Hagman
    Hagman Heating and Cooling (Rheem Dealer)
    Altoona, Iowa
    NOW
    ProSite Home Inspections


  7. #7
    Join Date
    Mar 2007
    Location
    Charlotte, NC
    Posts
    112

    Default Re: HVAC New Installation

    Broke for lunch.