Results 1 to 3 of 3
  1. #1

    Default Trip Tie Required?

    Greetings HI's,

    I'm sure this is covered in Elec101, so thank you for being patient.
    I performed an 11 month inspection on a home today and saw what I believed to be 4-wire romex with one wire connected to a 20amp breaker for the disposal and the other connected to a separate 20amp breaker for the dishwasher. They share a single neutral and ground.
    Question: Should there be a trip tie between the breakers?

    Additional comments are welcome.

    Thanks,
    Michael - Scher Professional Inspections- Austin Real Estate Inspector
    Scher Professional Inspections

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Tampa, Fl
    Posts
    155

    Default Re: Trip Tie Required?

    If they are in the same outlet/junction box they need a common trip.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,040

    Default Re: Trip Tie Required?

    If on the same yoke/strap (i.e., a duplex with disposer and dishwasher - both on same device) - tie handle required.

    Could be in same box and tie handle not 'required' - but a really, really, good idea.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •