	05-05-2007, 02:19 PM #1 trap trapdon't we need a trap at all condensate drains? 
 Similar Threads:
 
- 
	05-05-2007, 02:47 PM #2 Re: trap Re: trapThe pump is considered the trap. I would recommend the lines be run separate for drain lines, I can not tell if the shut off is wired for the pump, so that it will turn the furnace and A/C off if the pump stops working if this is in a living space. 
 
 
- 
	05-05-2007, 07:55 PM #3 Re: trap Re: trapYes. 
 
 I've never seen a condensate pump installed such that it meets the requirements of a trap.
 
 There should be a trap between the AHU and the condensate pump.
 
 
- 
	05-06-2007, 12:05 PM #4 Re: trap Re: trapWe always putt a trap before the condensate pump. that setup in the picture will stink up the house during the heating season. this is why you should put it there 
 
 
- 
	05-06-2007, 12:11 PM #5
 


 
 
					
					
 
				
				
				