Results 1 to 5 of 5

Thread: trap

  1. #1
    Join Date
    Mar 2007
    Location
    Connecticut
    Posts
    1,828

    Default trap

    don't we need a trap at all condensate drains?

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Mike Huppi's Avatar
    Mike Huppi Guest

    Default Re: trap

    The pump is considered the trap. I would recommend the lines be run separate for drain lines, I can not tell if the shut off is wired for the pump, so that it will turn the furnace and A/C off if the pump stops working if this is in a living space.


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: trap

    Yes.

    I've never seen a condensate pump installed such that it meets the requirements of a trap.

    There should be a trap between the AHU and the condensate pump.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Chris Ethridge's Avatar
    Chris Ethridge Guest

    Default Re: trap

    We always putt a trap before the condensate pump. that setup in the picture will stink up the house during the heating season. this is why you should put it there


  5. #5
    Mr Bill's Avatar
    Mr Bill Guest

    Default Re: trap

    Quote Originally Posted by Jerry Peck View Post
    Yes.

    I've never seen a condensate pump installed such that it meets the requirements of a trap.

    There should be a trap between the AHU and the condensate pump.
    Your exactly right and if you look at the picture how is that pump set up going to keep out any odors? JMHO