    Default water heater expansion tank

    when Inspected a hot water heater that does not have a expansion tank installed, is it correct to recommend a expansion tank be installed for safety and proper operations, some communitys require a tank added when the older water heater is replaced.

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: water heater expansion tank

    It depends on the code the water heater is under. IRC only requires an expansion device when there is a closed system (check valve.) If no closed system, no thermal expansion device is required, of course if you live in the land of slab foundations with pressure regulators buried in the yard it is really difficult to know.
    I always measure the static water pressure and recommend installation of a pressure regulator and expansion tank if the pressure is more than 80 PSI.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Santa Rosa, CA
    Posts
    3,154

    Default Re: water heater expansion tank

    Quote Originally Posted by daniel nantell View Post
    when Inspected a hot water heater that does not have a expansion tank installed, is it correct to recommend a expansion tank be installed for safety and proper operations, some communitys require a tank added when the older water heater is replaced.
    Like Jim said. I believe it is also required when the house is on a well. Maybe not if it is gravity fed, but when there is a bladder tank. This would be true with homes that have a booster pump as well.

    Department of Redundancy Department
    Supreme Emperor of Hyperbole
    http://www.FullCircleInspect.com/

  4. #4
    Join Date
    Mar 2007
    Location
    Charlotte NC Licensed in NC and SC
    Posts
    597

    Default Re: water heater expansion tank

    I can't think of the right term, but if the system has a small bleeder valve with a small clear hose usually to the exterior this takes the place of the expansion tank. I see these on many new homes.


  5. #5
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: water heater expansion tank

    Quote Originally Posted by Bruce King View Post
    I can't think of the right term, but if the system has a small bleeder valve with a small clear hose usually to the exterior this takes the place of the expansion tank. I see these on many new homes.
    It is an expansion valve, it is less expensive than a tank and it's purpose is the same as a tank. You just need to have a place to put the water that comes out of the valve(tube). On my home it goes outside, right next to my TPR discharge line.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  6. #6
    Paul Johnston's Avatar
    Paul Johnston Guest

    Default Re: water heater expansion tank

    Quote Originally Posted by Gunnar Alquist View Post
    Like Jim said. I believe it is also required when the house is on a well. Maybe not if it is gravity fed, but when there is a bladder tank. This would be true with homes that have a booster pump as well.
    If you have a well, bladder tank and no check valve why would you need an expansion tank?


  7. #7
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: water heater expansion tank

    You have a foot valve but that is before the bladder and you would think the bladder tank would be the same as a expansion tank. From what I have read a 40 gallon water tank will expand a half gallon.

    So what's the verdict plumbers, do you need a expansion tank on a well system?

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  8. #8
    Join Date
    Jun 2008
    Location
    Stacy, MN
    Posts
    148

    Default Re: water heater expansion tank

    Per the IRC an expansion tank is not needed for a water heater, whether there is a well, or it is city water. An expansion tank is required for a boiler as a part of a hydronic heating system:
    M2003.1 General.
    Hot water boilers shall be provided with
    expansion tanks. Nonpressurized expansion tanks shall be
    securely fastened to the structure or boiler and supported to
    carry twice the weight of the tank filled with water. Provisions
    shall be made for draining nonpressurized tanks without emptying
    the system.

    M2003.1.1 Pressurized expansion tanks.
    Pressurized
    expansion tanks shall be consistent with the volume and
    capacity of the system. Tanks shall be capable of withstanding
    a hydrostatic test pressure of two and one-half times the
    allowable working pressure of the system.

    M2003.2 Minimum capacity.
    The minimum capacity of

    expansion tanks shall be determined from Table M2003.2.

    First post, be kind!



  9. #9
    Join Date
    Mar 2007
    Location
    Philadelphia PA
    Posts
    3,177

    Default Re: water heater expansion tank

    From a thread in the archives:

    IRC P2903.4 Thermal Expansion. In addition to the required pressure relief valve, an approved device for thermal expansion control shall be installed on any water supply system utilizing storage water heating equipment whenever the building supply pressure is greater than the required relief valve pressure setting or when any device, such as a pressure reducing valve, backflow preventer or check valve, is installed that prevents pressure relief through the building supply. The thermal expansion device shall be sized in accordance with the manufacturer's installation instructions.


  10. #10
    Join Date
    Jun 2008
    Location
    Stacy, MN
    Posts
    148

    Default Re: water heater expansion tank

    That section has been amended in the 2006 IRC:

    P2903.4 Thermal expansion control.
    A means for controlling increased pressure caused by thermal expansion shall be installed where required in accordance with Sections P2903.4.1 and P2903.4.2.

    P2903.4.1 Pressure-reducing valve.
    For water service system sizes up to and including 2 inches (51 mm), a device for controlling pressure shall be installed where, because of thermal expansion, the pressure on the downstream side of a pressure-reducing valve exceeds the pressure-reducing valve setting.

    P2903.4.2 Backflow prevention device or check valve.
    Where a backflow prevention device, check valve or other device is installed on a water supply system using storage water heating equipment such that thermal expansion causes an increase in pressure, a device for controlling pressure shall be installed.





  11. #11
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,851

    Default Re: water heater expansion tank

    Just take a few seconds and think about the water heater and what is connected to it. If the water inlet line has any device that has a "check" valve or device that keeps the water from backing up the line then you need to have an expansion tank or valve on the line.

    The water expands in the water heater, it has to go somewhere so it can't then you need something that will allow it to expand.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  12. #12
    Join Date
    Mar 2007
    Location
    Fuquay Varina, NC
    Posts
    1,074

    Default Re: water heater expansion tank

    Scott,
    So if I am reading into to this right, if it's on a well and there is no check valves after the bladder tank a Expansion tank is not needed........

    A bladder tank has lots of room for expansion does it not?

    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com

  13. #13
    Join Date
    Jun 2008
    Location
    Stacy, MN
    Posts
    148

    Default Re: water heater expansion tank

    Mike, use this link: http://www.blueridgecompany.com/docu...mExpansion.pdf
    It shows installation requirements for when a tank is required, it also shows a cut away of expansion tanks, a well pressure tank is constructed the same way as a expansion tank. I think your covered unless a check valve is installed between the pressure tank and the water heater.