    Default Ledger Attachment

    This is from new construction... I said it's most likely incorrect and would need to be approved by an engineer.

    The ledger has several small spacers that place is 1.5" out from the rim joist. Most of the lag bolts are left spanning this gap. I'm not sure what the point of the nuts and washers is. Maybe an attempt to keep the bolts from bending??

    Even my caviat of 'most likely' is pretty generous, I'm thinking.

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2

    Default Re: Ledger Attachment

    It's a good idea to space the ledger out slightly, but that takes spacing to a whole new level. I would have written that up as well.


  3. #3
    Join Date
    Mar 2007
    Location
    Oregon
    Posts
    2,365

    Default Re: Ledger Attachment

    The other crazy thing was that I was only able to identify 3 bolts coming through from in the crawl... meaning that the others (probably 10+) were screws of unknown depth and ended who knows where.


  4. #4
    Join Date
    Feb 2008
    Location
    Caledon, Ontario
    Posts
    4,982

    Default Re: Ledger Attachment

    The washers are to stop the nut from eating into the wood as it tightened. This allows the nut to be torqued tighter.


  5. #5
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Ledger Attachment

    Depending on the construction the 2007 IRC supplement my specify a max of 1/2" between "the face of the face of the ledger board and face of the wall sheathing", see table R502.2.2.1, notes 2 and 8 here:

    http://www.deckmagazine.com/pdf/2007/0707/0707ledg.pdf

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ledger Attachment

    Quote Originally Posted by Michael Thomas View Post
    Depending on the construction the 2007 IRC supplement my specify a max of 1/2" between "the face of the face of the ledger board and face of the wall sheathing", see table R502.2.2.1, notes 2 and 8 here:
    Michael,

    A better statement would be:

    2 The maximum gap between the face of the ledger board and face of the wall sheathing shall be
    1⁄2".

    with the information that the note 2 was relating to:

    Joist Span (ft) ------------- 6' and less --- 6'-1" to 8' --- 8'-1" to 10' --- 10'-1" to 12' --- 12'-1" to 14' --- 14'-1" to 16' --- 16'-1" to 18'
    Connection Details ---------- On-Center Spacing of Fasteners 4,5
    1⁄2" diameter bolt with ------ 36 ------------ 36 ------------- 29 ------------- 24 ---------- 21 ------------ 18 ----------- 16
    15⁄32" maximum sheathing and
    1⁄2" stacked washers2,8

    With the key to that allowance being " 1⁄2" diameter bolt with 15⁄32" maximum sheathing and 1⁄2" stacked washers "

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ledger Attachment

    What's with all those holes in the face and edge of that ledger.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Ledger Attachment

    Jerry,

    What surprised me was the extra 1/2" allowed in note 8 - how much support against shear is supplied (for example) by gypsum board?

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  9. #9

    Default Re: Ledger Attachment

    What's with all those holes in the face and edge of that ledger.
    Jerry,

    That's what our pressure treated wood looks like. Look at the joists and you will see the same thing.


  10. #10
    Ted Menelly's Avatar
    Ted Menelly Guest

    Default Re: Ledger Attachment

    Quote Originally Posted by Jerry Peck View Post
    What's with all those holes in the face and edge of that ledger.
    No problem with the holes. Its just pine wood boring beetles eating the soft wood getting a snack


  11. #11
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: Ledger Attachment

    Quote Originally Posted by Michael Thomas View Post
    What surprised me was the extra 1/2" allowed in note 8 - how much support against shear is supplied (for example) by gypsum board?
    Michael,

    That was my first thought too, then I realized it is not just an "extra 1/2 inch", it is a totally different setup.

    In note 2, the 1/2" can be made up with "stacked washers" - unfortunately, no mention of their outside diameter was made, I would think they would want fender washer sized washers, not regular small outside diameter washers, but, that was not mentioned (or I've missed it).

    However, in note 8, there is no "cantilevering" as such (in note 2 the bolts are are cantilevered out that 1/2", with the stacked washers supporting the "cantilevered" distance) as the exterior sheathing is required to be full thickness, up to the maximum thickness of 1". That means that the ledger is pulled snug to the sheathing with friction between the sheathing and the ledger being used to distribute the load to the sheathing above and below (unlike a "cantilevered" bolt, which is trying to shear itself off or 'bend' the bolt).

    I guess until the gypsum is either crushed (easy to do with a washer and a nut, but much harder to do with a ledger distributing the load of that washer and nut) or is wet (and it is assumed that the gypsum sheathing will not get wet, after all, it is supposed to be properly flashed, and the wall above is properly weatherproofed (in whatever manner is appropriate for the siding/veneer used). Thus, dry gypsum will support quite a bit when the load is placed over a large enough area. At least that was my thoughts on it.

    However, it also includes "foam" sheathing, is that even as strong as gypsum? If so, then the above would apply to it. If not, I'm out of ideas.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com