    Greetings Friends;

    I did an inspecton yesterday, it was inspected about a year ago by another inspector, who evidentaly called out clearance issues on the
    B vent for the furnace. In the photo showing the rafter there is about 1/2 inch of clearance between the vent pipe and the flashing nailed around the truss. at the roof the extra flashing appears to be just jammed up between the vent pipe and the roof deck. What do you think, I do not believe just jamming a piece fo extra flashing up there is adequate and extra distance needs to be in place.

    Thanks Willie

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Inspection Referral

  2. #2

    Default Re: B vent clearance

    There has to be an air space between the combustible material at flashing/ deflection shield for that to work.


  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Exclamation Re: B vent clearance

    Stated clearances are air spaces. However, NFPA 211 does not recognize clearance reduction less than 12 inches even with a ventilated shield.

    The shields shown will act to either:
    a) conduct heat if in direct contact
    b) provide a target to absorb more radiant heat than had it been left alone
    c) impeded what little cooling air flow there was
    d) are a violation of the codes and listing.

    HTH,

    Keep the fire in the fireplace.

  4. #4
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: B vent clearance

    Quote Originally Posted by Bob Harper View Post
    Stated clearances are air spaces. However, NFPA 211 does not recognize clearance reduction less than 12 inches even with a ventilated shield.

    The shields shown will act to either:
    a) conduct heat if in direct contact
    b) provide a target to absorb more radiant heat than had it been left alone
    c) impeded what little cooling air flow there was
    d) are a violation of the codes and listing.

    HTH,
    Mr. Harper,

    Would not the B vent clearance be 1 inch to combustibles not 12 inches ?
    .

    Attached Files Attached Files
    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  5. #5
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Exclamation Re: B vent clearance

    Sure, B-vent carries a 1 inch clearance to combustibles. Those same listed instructions you referenced also warn you against tampering with their product or installing it outside the listed instructions.

    Billy, my point is those clearance reduction systems with the ventilated heat shields derived from NFPA 211 12.6.2 were intended for solid fuel appliances. Within solid fuel appliances, the maximum reduction must still leave at least 12" to the combustible. Over the years, the concept of a heat shield with a 1" ventilated air space has been loosely applied and adopted to gas, oil and other heat related applications. Your AHJ can rule on what he accepts or not. However, I know of no application that can reduce B-vent to less than 1", listed or otherwise.

    HTH.

    Keep the fire in the fireplace.

  6. #6
    William Mize's Avatar
    William Mize Guest

    Default Re: B vent clearance

    Thanks Guys

    I thought the bandaid approach was not proper I will call the local AHJ this morning and get his thoughts. It never fails, it is easier to do it right than to go back and redo.

    I will advise my customer as to the consensus of this group. and MY thoughts.

    Thanks Again

    willie


  7. #7
    Join Date
    Aug 2008
    Location
    Pleasant Hill, Iowa
    Posts
    145

    Default Re: B vent clearance

    This is an improper B-Vent installation at the top and at the sheet metal flashing. A B-Vent must have a 1 inch clearance to combustables, FYI- and a single wall Vent Connector from the appliance to the B-Vent must have a 6 inch clearance to combustables. This is a easy fix! I can see a connection just below the lower metal flashing, an offset elbow would provide the proper clearance and re-cut the roof deck and move over the flashing 1 - 2 inches would take care of this problem. This is a 2 hour job at the most.