    Default 1957 UPGRADED ELECTRICAL SERVICE

    Hey all

    hope business is keeping food on the table--fore the first time i am alittle slow---maybe four inspection a week.

    but here is a 1957 home i did today,and have to go back on sat for full inspection. but over head service seems suspect,and main box,was upgraded,and i have called city to see if permit and inspection completed. they haven't called back yet.

    70 amp service,and main service wires seem suspect to me and how about that splice or tap {wire nuts}

    i tried to take clear picture of that service entry wire to main-but it is blurry,,will retake sat,,,would you call that romex

    thanks
    charlie
    doies that main wire with ground wire cut back seem right,i have never seen this before,,
    any help here

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Chris Kynard's Avatar
    Chris Kynard Guest

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Why did they stop the mast under the soffit? What kind of anchoring do the cables have? Looks like a crappy amateur installation from the pics.


  3. #3
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    "electrically heated gutters"

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  4. #4
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Charlie,

    That overhead electrical service tie-in to roof mounted insulators is not only not allowed (not allowed by code), it is not safe either.

    When the electrician upgraded the service equipment the service mast and overhead service should also have been replaced and not only made safe, but made code compliant too.

    No need to retake any photos, that service needs to be replaced.

    Stupid idiot electrician (wait, no electrician would do that ) cut the friggin' ground wire off at the sheath, sheesh!

    However, that is the least of the problems.

    My guess is that the service equipment was originally inside the house, and now this panel, as installed, becomes "service equipment".

    Here are a few things wrong in that service equipment:

    - neutral conductor multiple tapped at the neutral terminal bus bar

    - the panel inside to which that mess in the bottom is running to is now no longer "service equipment", it is now "not service equipment". That means that the neutrals and grounds are no longer allowed to be tied together at that interior panel, or between that interior panel and the service equipment

    - what were 'service entrance conductors' (that mess at the bottom) are now 'feeder conductors' and with feeder conductors, the neutral conductor is required to be isolated from ground and insulated - the original 'service entrance cable' does not have an insulated neutral, thus, that feeder now needs to be replaced with a wiring method which includes both a grounding conductor and an insulated neutral conductor

    - by the looks of it, there was a grounding conductor terminal bar on the left, and it and the cross over bar have been removed, leaving the neutral terminal bar being held in place only with plastic snap in prongs - the label most likely shows a grounding bar on the left and a cross over bar between the grounding terminal bar and the neutral terminal bar, which would need to be left in place as it helps hold the two terminal bars in place

    - it looks like the concentric knock-out in the lower right side is pulling out and needs to be repaired, along with an insulating bushing

    Two pluses I see in your photo:

    1) They could actually read and 'Top" is on top.

    2) The enclosure was mounted with the proper mounting feet. This leaves the required 1/4" air space between the back of the enclosure and the brick wall.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  5. #5
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Jerry,

    Why is that panel not considered service equipment?
    It looks like it is the main point of entry and is connected to a main breaker.

    Is it because main service wire should have an uninsulated neutral/ground wire? Is that a code issue?

    Thanks


  6. #6
    Join Date
    Mar 2007
    Location
    Vancouver - Canada
    Posts
    225

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    In addidtion to all of Jerry's comments... Is that home a rancher ?? Just wondering what the ground clearance is to all the overhead cables. Also, is there a main breaker upstream from that panel or do the mains just come in onto the loadcentre's main lugs ?


  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Quote Originally Posted by Ken Amelin View Post
    Jerry,

    Why is that panel not considered service equipment?
    It looks like it is the main point of entry and is connected to a main breaker.
    Quote Originally Posted by Jerry Peck View Post
    My guess is that the service equipment was originally inside the house, and now this panel, as installed, becomes "service equipment".
    Ken,

    If by "that panel" you mean the one in the photo, it is service equipment, see my quote above.

    The problem - ONE OF the problems - is that the interior panel 'was' service equipment at one time, and was fed by the service entrance conductors. Since the addition of "that panel" on the exterior, the interior panel is no longer the service equipment, thus it is fed by feeder conductors, not service entrance conductors, and feeder conductors, like branch circuit conductors, must have the neutral insulated and must have a separate ground path (either metal conduit or a grounding conductor).

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  8. #8
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,152

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    GUYS
    got a peek inside this house today, and there it was the original service equipment and it was of the federal pacific beast,,i'm interested in seeing the wiring inside that panel

    charlie

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images

  9. #9
    Join Date
    Mar 2007
    Location
    Cape Cod, Massachusetts
    Posts
    614

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Jerry,

    You've got good eyes.

    After going back and looking again at the pictures, I can see what looks like the top of the "service equipment" panel on the exterior. (I didn't see that at first glance)

    I now understand your comments.

    But this just begs me to ask more questions.
    Let say there was no exterior panel and the interior panel was the service equipment.

    1. Would service wire splices be allowed within the panel, prior to the main breaker?

    2. If yes, is it OK to have the bare service neutral wire spliced to an insulated white wire?

    Thanks


  10. #10
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    No & no.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  11. #11

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Jerry Peck No & no. Today 09:48 AM Ken Amelin Jerry,

    You've got good eyes.

    After going back and looking again at the pictures, I can see what looks like the top of the "service equipment" panel on the exterior. (I didn't see that at first glance)

    I now understand your comments.

    But this just begs me to ask more questions.
    Let say there was no exterior panel and the interior panel was the service equipment.

    1. Would service wire splices be allowed within the panel, prior to the main breaker?

    2. If yes, is it OK to have the bare service neutral wire spliced to an insulated white wire?

    Thanks
    Jerry, do you have a code reference for that, or other data to back it up that you could share. Reason I ask is I have seen service wires spliced in a panel a few times over the years and have been told it is OK...

    Thanks


  12. #12
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,032

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Quote Originally Posted by Brandon Whitmore View Post
    Jerry, do you have a code reference for that, or other data to back it up that you could share. Reason I ask is I have seen service wires spliced in a panel a few times over the years and have been told it is OK...

    (slaps forehead with hand - knuckle head you ... he says to himself)

    "over the years and have been told it is OK"

    Over the years it was not okay, and that is what I keep remembering, ... then the code changed from 'shall not be spliced' (with a few exceptions) to 'splices shall be ... '.

    That's the part I keep forgetting - the old electrician in me says 'remember *shall not be spliced* ' and the inspector part keeps forgetting the code now allows service entrance conductors to be spliced, if properly done with proper splicing devices.

    Me bad, again.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  13. #13
    John Steinke's Avatar
    John Steinke Guest

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    I see some issues here that have come up in several recent threads. So, I'll start at the very beginning ....

    Service requirements are determined by the local utility, and not the NEC. Those requirements do change over time; when you replace the service, you need to comply with the latest requirements.

    The use, by the PoCo, of separate overhead wires is quite dated; for that type of service drop, though, attaching each wire to a separate, securely mounted insulator is proper.
    Likewise, ending the service mast below the eave was once the preferred way to do it. One of the reasons was that none of the mast was concealed by passing through the eave and roof; it's simply amazing what folks have done in order to steal power.
    Some areas don't even have a mast; SE cable is used from roofline to panel.

    Using wire nuts to make the existing wires reach the breaker is allowed.
    Not connecting the ground wires is not allowed. I can't tell if there is a disconnect before the panel.

    All that said, what I would expect to see for this service change is:
    1) A ground rod;
    2) A mast of 2" rigid, projecting above the roof about 30". (The mast doesn't HAVE to go through the roof; bending it is allowed);
    3) The mast to be bot vertical and secured in place;
    4) The PoCo wires to be 'triplex" (two insulated wires wound around a steel reinforced bare aluminum wire); and,
    5) A ground buss.

    What I suspect you have is a "service change" made without permit, by an unqualified person.


  14. #14
    Join Date
    Mar 2007
    Location
    Tampa, Fl
    Posts
    155

    Default Re: 1957 UPGRADED ELECTRICAL SERVICE

    Without a doubt, call it out! Among everything else, could you imagine the homeowner cleaning the gutters and contacting those non-insulated links? Or, how about clogged gutters that have ice hanging, water pouring from them and contact the non-insulated links and energizing any nearby metal.