Results 1 to 11 of 11
Thread: Notch in rafter
    mathew stouffer's Avatar
    mathew stouffer Guest
    Default Notch in rafter
    This is borderline, would you call this out?
    Mat
    Default Re: Notch in rafter
    Mat
    Is the notch wider than 1/3 the depth of the rafter?
    Ron Bibler's Avatar
    Ron Bibler Guest
    I would. if that ever splits it could come back on you... Is that pipe up on the rafter?
    Best
    Ron
    Brent Simmerman's Avatar
    Brent Simmerman Guest
    I agree with Ron, I would call it out.
    Nampa, Idaho
    I don't believe I would call that out.
    Ron Bibler's Avatar
    Ron Bibler Guest
    Trent you can make a note: about anything. I think that its just smart to make notes on just about everything that is not perfect or if its been adjusted in some way. but thats me.
    Best
    Ron
    Thansk guys. I found a section in the code which states it is acceptable.
    Hi, Guys &
    Definitely 'Butchered"...
    I'd sure call it !
    CHEERS
    -Glenn Duxbury, CHI
    Fuquay Varina, NC
    Allot light around those pipes. Is the roof flashings in place.
    If it was within guidlines it wouldn't go in my report.
    Mike Schulz License 393
    Affordable Home Inspections
    www.houseinspections.com
    Sep 2008
    Texas
    There are other rafters that are close enough to it AND it is within the allowed notch (your statement) Then no reason to call it out.
    Richard M. Pinkerton's Avatar
    Richard M. Pinkerton Guest
    IBC 2006- "2308.10.4.2 Notches and holes.
    Notching at the ends of
    rafters or ceiling joists shall not exceed one-fourth the
    depth. Notches in the top or bottom of the rafter or ceiling
    joist shall not exceed one-sixth the depth and shall not be
    located in the middle one-third of the span, except that a
    notch not exceeding one-third of the depth is permitted in
    the top of the rafter or ceiling joist not further from the
    face of the support than the depth of the member."
    Pretty much says it all.
