Thread: Partial cut.

  1. #1
    Eric Shuman's Avatar
    Eric Shuman Guest

    Default Partial cut.

    One year old home. There is a partial cut in the top of this I-Joist. It goes from about 1/2 inch at one side of the the flange to nothing at the other side (first photo). The joist is well supported by top plates below. The builder had the truss manufacturer's "Strategic Sales Rep" (not the manufacturer's engineer) out to to have a look and he said no problem. The builder did have an engineer come out as well. The only comment the engineer made was "I defer to the Truss rep's opinion" but would not address the issue himself.

    The floor sheathing was cut out at this area because of a large dip in the floor that the homeowner was concerned about. Turns out that where sets of floor trusses meet up perpindicular to each other, the tops of the flanges were not at the same heights (about 1/2 inch difference at the meeting point, second photo) which was causing the sheating to dip down rather noticeably. I'm not sure why the truss tops were not flush other than poor workmanship.

    Customer wants to know if they should get an engineer's letter stating that there is nothing wrong here. So far no one wants to put anything in writing. My thought is engineer inspection and a written statement that this area either is, or is not problematic structurally

    Any thoughts?

    Thanks,

    Eric

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    Crawl Space Creeper

  2. #2
    Join Date
    Mar 2007
    Location
    Plano, Texas
    Posts
    4,245

    Default Re: Partial cut.

    There is a reason no one wants to put anything in writing... they don't want the liability... do you?
    I would recommend something in writing from an engineer or replacement of the damaged component(s), their choice. There is an obvious problem with the installation and the cut in the Joist did not help.

    Jim Luttrall
    www.MrInspector.net
    Plano, Texas

  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,042

    Default Re: Partial cut.

    Quote Originally Posted by Eric Shuman View Post
    There is a partial cut in the top of this I-Joist. It goes from about 1/2 inch at one side of the the flange to nothing at the other side (first photo).
    Eric,

    That cut was made with a saw blade, obviously, and saw blades make a saw cut (kerf) the same width all the way across the cut.

    That angled cut means the top 2x as deflected in two directions: 1) bowed to one side, closing the cut up on the concave side; 2) deflected down, closing the cut up at the top.

    Don't you love it when someone buys a new circular saw and becomes a 'carpenter' ... hmmmmm, if I set this blade all the way down, I know it will be deep enough to cut through that floor sheathing ...

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  4. #4
    Join Date
    Aug 2007
    Location
    Memphis TN.
    Posts
    4,311

    Default Re: Partial cut.

    Quote Originally Posted by Eric Shuman View Post
    The builder had the truss manufacturer's "Strategic Sales Rep" (not the manufacturer's engineer) out to to have a look and he said no problem.

    The only comment the engineer made was "I defer to the Truss rep's opinion" Turns out that where sets of floor trusses meet up perpindicular to each other, the tops of the flanges were not at the same heights (about 1/2 inch difference at the meeting point, second photo) Eric
    Eric,

    Strategic As IN I NEED TO KEEP SELLING THIS GUY MY STUFF! Did He also say the
    truss was installed to manufactures instructions? Is toenailing 2 nails the proper install method for his product?

    It Might have Choked Artie But it ain't gone'a choke Stymie! Our Gang " The Pooch " (1932)
    Billy J. Stephens HI Service Memphis TN.

  5. #5
    Eric Shuman's Avatar
    Eric Shuman Guest

    Default Re: Partial cut.

    Quote Originally Posted by Jerry Peck View Post
    Eric,

    Don't you love it when someone buys a new circular saw and becomes a 'carpenter' ... hmmmmm, if I set this blade all the way down, I know it will be deep enough to cut through that floor sheathing ...
    Yeah, looks like the top of one of my wooden sawhorses.

    Quote Originally Posted by Billy Stephens View Post
    Eric,

    Strategic As IN I NEED TO KEEP SELLING THIS GUY MY STUFF! Did He also say the
    truss was installed to manufactures instructions? Is toenailing 2 nails the proper install method for his product?
    Yeah, or as in, the strategy is to shut the homeowner up.

    I would have been more impressed if his business card had P.E. written on it instead of Strategic Sales Rep.

    I noticed the toenails too. I would think it should have been blocked at the end to prevent rotation.

    Eric


  6. #6
    Join Date
    Mar 2007
    Location
    Chicago, IL
    Posts
    2,797

    Default Re: Partial cut.

    I thought this was pretty amusing...

    Tray ceiling

    Michael Thomas
    Paragon Property Services Inc., Chicago IL
    http://paragoninspects.com

  7. #7
    Mike Truss Guy's Avatar
    Mike Truss Guy Guest

    Default Re: Partial cut.

    You can often get around getting engineering if you sister another complete I-joist next to the cut one.