    Ron Bibler's Avatar
    Ron Bibler Guest
    Default Are these to close?
    Inspection today and these 2 are next to each other.
    The box above the gas is the 200AMP main service.
    Best
    Ron
    Default Re: Are these to close?
    Ron,
    More than just too close, the gas meter is in the REQUIRED working space in front of the electrical equipment.
    Ron Bibler's Avatar
    Ron Bibler Guest
    Thanks Jerry. I was thinking i saw something one time about gas and the panel a fire hazard ?
    Best
    Ron
    * attachment
    Attached Files Attached Files
    James Billings's Avatar
    James Billings Guest
    Quote Originally Posted by Ron Bibler View Post
    Best
    Ron
    Hi Ron,
    The mandated working clearance is not always a fire hazard, though certainly a gas meter and especially the vent could create just that. The working clearance is to allow for working on equipment and has some safety issues involved. Once equipment is opened up, there is often exposed live parts. QUOTE FROM NEC (are we allowed to do this - quote the NEC?)
    "(3) Height of Working Space The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment."
    UNQUOTE
    This working clearance is a minimal requirement and changes if the object opposing the face of the panel is grounded, and may also vary with respect to voltage and amperage:
    QUOTE FROM NEC
    "Exhibit 110.18 Working space with one entrance. Only one entrance is required if the working space required by 110.26(A) is doubled. See Table 110.26(A)(1) for permitted dimensions of X.
    Table 110.26(A)(1) Working Spaces
    Nominal Voltage to Ground Minimum Clear Distance
    ...............Condition1.......... Condition 2........ Condition 3
    0–150........900 mm (3 ft)..... 900 mm (3 ft)...... 900 mm (3 ft)
    151–600......900 mm (3 ft).....1.1 m (31/2).........1.2 m (4 ft)
    Note: Where the conditions are as follows:
    Condition 1 — Exposed live parts on one side of the working space and no live or grounded parts on the other side of the working space, or exposed live parts on both sides of the working space that are effectively guarded by insulating materials.
    Condition 2 — Exposed live parts on one side of the working space and grounded parts on the other side of the working space. Concrete, brick, or tile walls shall be considered as grounded.
    Condition 3 — Exposed live parts on both sides of the working space."
    UNQUOTE
    Isn't the concrete, tile, brick, etc., an interesting point?
    james
    Last edited by James Billings; 12-29-2008 at 09:30 AM. Reason: spelling/ quote NEC
    Sep 2008
    Texas
    It may have been okay at the start of things. The electrical could have been there prior to the gas meter or the porch and railings.
    Still it violates the NEC...just may have been caused by the plumber or whoever built the porch. They probably didn't know that they were creating a problem.
    Greg Kelsey's Avatar
    Greg Kelsey Guest
    The location of the gas meter and its components relative to the location of the electrical meter is improper and a safety concern. The potential for a gas leak and an electrical overcurrent and arc is present which could be catastrophic. I believe the clearance minimum is 3 ft.
    Greg in VT
