View Full Version : Another panel question



mathew stouffer
09-08-2009, 06:57 AM
The house was built in 1903, obviously changes were made. This is the service disconnect with a 100amp. The neutrals and grounds are on the same bar, but I could not find an equipement ground. Needed some more eyes:)

John Arnold
09-08-2009, 07:04 AM
The grounds that are on the same bar as the neutrals are equipment grounds. Do you mean you didn't see a grounding electrode conductor?

Jim Port
09-08-2009, 07:22 AM
Looks like the GEC is to the left of the PVC conduits. It also looks like you can see where it bends just to the left of the bottom left breaker.

If you are looking for grounding conductors for wiring run in 1903 it will take awhile. That would pre-date grounded circuits.

mathew stouffer
09-08-2009, 07:32 AM
Should have proof read that, yes the GEC. But the house was rewired.

David OKeefe
09-08-2009, 08:21 AM
This is what Jim pointed out.

Jim Port
09-08-2009, 08:42 AM
Thanks David, exactly what I saw.

How did you insert those arrows?

David OKeefe
09-08-2009, 09:26 AM
I got it here.