PDA

View Full Version : A/C Disconnect boxe:



Jeff Eastman
09-29-2007, 12:21 PM
..........

Jerry Peck
09-29-2007, 01:44 PM
While I don't like that, there is no switch or overcurrent device in there, so it's okay.

Billy Stephens
09-29-2007, 01:46 PM
Jeff,

See Mr. Peck above.

Billy Stephens
09-29-2007, 01:53 PM
Mr Peck,

If there are fuse's in the disconnect then it would be an over current device.

Jerry Peck
09-29-2007, 07:16 PM
Mr Peck,

If there are fuse's in the disconnect then it would be an over current device.

You are, of course, correct *IF fused*, however, that photo looked like it was just a non-fused pull out disconnect. Meaning NO overcurrent protection.

Jerry Peck
09-29-2007, 07:20 PM
Should not those whites be labeled hot?

Dan,

Those whites look like the neutrals of the black & white circuit passing through. At least that's what I took them to be.

Which is one of the very reasons the whites are required to be "permanently reidentified by painting" or other effective (permanent) means *IF* they are part of a 240 volt circuit and not the neutrals for a 120 volt circuit.

You'd need to ask Jeff if he checked that as we cannot tell from the photo.

Billy Stephens
09-30-2007, 06:57 AM
however, that photo looked like it was just a non-fused pull out disconnect. Meaning NO overcurrent protection.

Mr. Peck,

Thanks. I can see the panel does not look deep enough.:)