    Saw this yesterday: a rubber natural gas extension running from furnace to fireplace.
    First of all, there's no clamp on the rubber hose. Second, it's a rubber hose used in an interior bathroom.
    73.jpg
    It runs through the house:
    gasline1.jpg
    To the outside - directly below a sliding glass door, back inside to the fireplace.
    30.jpg
    Any recommendations or further problems seen here?
    Thanks.

    -Geoffrey Smith

    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: One of the worst I've seen!

    That is CSST with a lightning strike outer covering - it is made for gas - it is not what you described it to be.

    Now, the installation of it is ... well ... leaves A LOT to be desired.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  3. #3
    Join Date
    Mar 2012
    Location
    Lansdale, PA
    Posts
    876

    Default Re: One of the worst I've seen!

    If you thought that was a rubber hose you need to spend more time during the inspection actually inspecting and not jumping to conclusions. Spending more time leaning about materials and methods would also be advisable.


  4. #4
    Geoffrey Smith's Avatar
    Geoffrey Smith Guest

    Default Re: One of the worst I've seen!

    Quote Originally Posted by Jerry Peck View Post
    That is CSST with a lightning strike outer covering - it is made for gas - it is not what you described it to be.

    Now, the installation of it is ... well ... leaves A LOT to be desired.
    Thanks Jerry. I appreciate it.