Results 1 to 3 of 3
  1. #1
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Gas Vent to Window Clearance

    Am I not mistaken in that there should be 10' of clearance between this gas vent (servicing a Versa indoor pool heater) and the 2nd floor bedroom window and or be at least 3' above the eave of the 2nd floor roof surface? I measured 6' from the window (while I was inside the bedroom)...

    http://i303.photobucket.com/albums/n...090814003p.jpg

    FYI (as I know it would probably get commented to otherwise), the gas vent you see on the lowest roof surface (pool room) that is next to the screen porch had been discontinued and was not being used.

    Similar Threads:
    Member Benefits1

  2. #2
    Join Date
    Feb 2008
    Location
    Iowa City, IA
    Posts
    108

    Default Re: Gas Vent to Window Clearance

    Advice, comments, thoughts would all be greatly appreciated!
    Thanks!


  3. #3
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: Gas Vent to Window Clearance

    I believe most have a horizontal clearance spacing requirement of 5 feet to any building opening, and that 5 feet horizontal would be vertically all the way up.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •