Results 1 to 9 of 9
Thread: Old House-No ARC faults
-
09-25-2009, 12:49 PM #1
Old House-No ARC faults
Anyone know if older electrical systems can be updated to include AFCI's? I suspected not but don't really know. Also, if AFCI breakers are available, I would think the cable assembly would need to have a ground conductor.
Similar Threads:
-
09-25-2009, 01:25 PM #2
Re: Old House-No ARC faults
Here is an excerpt from UL site. Grounds are not required.
The Carbonized Path Arc Ignition Test is a non-contact arcing test conductedbuilt over 40 years ago.
with NM-B cable with a series insulation cut. Tests are conducted with arcing
currents of 5 A, 10 A, rated current, and 150% rated current. The
Branch/Feeder, Combination, and Outlet Branch Circuit AFCIs are subjected to
the Carbonized Path Arc Ignition Test. The Outlet Branch Circuit AFCI is
subjected to the Carbonized Path Arc Ignition Test with the arcing occurring
upstream, to represent series arcing in the branch circuit wiring between the
origin of the branch circuit and the first outlet receptacle. The Outlet Branch
Circuit AFCI is also subjected to the Carbonized Path Arc Ignition Test using NMB
cable without a grounding conductor, as may be found in some older homes
-
09-25-2009, 06:53 PM #3
Re: Old House-No ARC faults
If the house has 12-3 wire sharing the neutral, those circuits will not be able to use the AFCI breakers. The ground is not necessary, as stated earlier.
Jim Robinson
New Mexico, USA
-
09-25-2009, 08:52 PM #4
-
09-26-2009, 07:14 AM #5
Re: Old House-No ARC faults
As I recall, having exchanged e-mails with Siemens (may have been Cutler-Hammer) they said that if the AFCI is rated 120 volts / 240 volts, then the AFCI will work on a multiwire circuit, however, if the AFCI is rated 240 volts (only, not 120 volts also) then the AFCI will not work on multiwire circuits.
-
09-26-2009, 10:24 PM #6
Re: Old House-No ARC faults
I'd be somewhat curious as to why there would be a 240 volt only AFCI when they are only required on 120 volt circuits. The NEC 2011 draft doesn't show any contemplated requirements for a 240 volt AFCI so the earliest possible requirement would be 2014.
Presently, Siemens is the only company I'm aware of marketing a 2 pole AFCI breaker, and it is available in one version (with 15 or 20 AMP ratings) designed to be used on multiwire (shared neutral) branch circuits. Siemens literature indicates the intent is the device be used on a multiwire circuit and it therefore can't be used on a 240 volt circuit because it isn't listed for the application.
What the 2011 draft DOES have is a requirement that would mandate an AFCI receptacle be installed, or the circuit be AFCI protected, when a receptacle would have to be AFCI protected because of location if the receptacle is replaced. This is like the current GFCI rule.
I look for MAJOR issues here when homeowners find out it's going to cost between $35.00 and $40.00 to change a receptacle and can virtually guarantee that people who would never dream of changing a receptacle will start doing so.
-
09-27-2009, 08:44 AM #7
-
09-27-2009, 07:45 PM #8
-
10-02-2009, 03:53 PM #9
Re: Old House-No ARC faults



Reply With Quote



Bookmarks