    Tampa, FL
    Default Old House-No ARC faults
    Anyone know if older electrical systems can be updated to include AFCI's? I suspected not but don't really know. Also, if AFCI breakers are available, I would think the cable assembly would need to have a ground conductor.
    Default Re: Old House-No ARC faults
    Quote Originally Posted by Tom McDonnell View Post
    Here is an excerpt from UL site. Grounds are not required.
    The Carbonized Path Arc Ignition Test is a non-contact arcing test conducted
    with NM-B cable with a series insulation cut. Tests are conducted with arcing
    currents of 5 A, 10 A, rated current, and 150% rated current. The
    Branch/Feeder, Combination, and Outlet Branch Circuit AFCIs are subjected to
    the Carbonized Path Arc Ignition Test. The Outlet Branch Circuit AFCI is
    subjected to the Carbonized Path Arc Ignition Test with the arcing occurring
    upstream, to represent series arcing in the branch circuit wiring between the
    origin of the branch circuit and the first outlet receptacle. The Outlet Branch
    Circuit AFCI is also subjected to the Carbonized Path Arc Ignition Test using NMB
    cable without a grounding conductor, as may be found in some older homes
    built over 40 years ago.
    New Mexico
    If the house has 12-3 wire sharing the neutral, those circuits will not be able to use the AFCI breakers. The ground is not necessary, as stated earlier.
    Apr 2009
    NY State
    There are some brands of two-pole AFCI breakers that work for this purpose. Some.....not many.
    As I recall, having exchanged e-mails with Siemens (may have been Cutler-Hammer) they said that if the AFCI is rated 120 volts / 240 volts, then the AFCI will work on a multiwire circuit, however, if the AFCI is rated 240 volts (only, not 120 volts also) then the AFCI will not work on multiwire circuits.
    Mar 2009
    Colorado Front Range
    I'd be somewhat curious as to why there would be a 240 volt only AFCI when they are only required on 120 volt circuits. The NEC 2011 draft doesn't show any contemplated requirements for a 240 volt AFCI so the earliest possible requirement would be 2014.
    Presently, Siemens is the only company I'm aware of marketing a 2 pole AFCI breaker, and it is available in one version (with 15 or 20 AMP ratings) designed to be used on multiwire (shared neutral) branch circuits. Siemens literature indicates the intent is the device be used on a multiwire circuit and it therefore can't be used on a 240 volt circuit because it isn't listed for the application.
    What the 2011 draft DOES have is a requirement that would mandate an AFCI receptacle be installed, or the circuit be AFCI protected, when a receptacle would have to be AFCI protected because of location if the receptacle is replaced. This is like the current GFCI rule.
    I look for MAJOR issues here when homeowners find out it's going to cost between $35.00 and $40.00 to change a receptacle and can virtually guarantee that people who would never dream of changing a receptacle will start doing so.
    Apr 2009
    NY State
    I was wondering the same thing.
    They may be making them for the overseas market, UK for example? They are an international company.
    I can just imagine British handymen in 300 year old brick cottages messing around with 240 volts, yikes!
    Quote Originally Posted by ben jacks View Post
    First up, code prior to the 1970's did not establish EGC connections for switches when the 3 prong receptacle came on the market...
    I am traveling and do not have access to my codes, but grounding to the metal strap of the switch came in at the same time grounding for receptacles came in, to my best recollection - I will need to verify that when I get back to my office toward the end of next week.