Thread: Wut's up with this vent?
08-06-2010, 09:15 PM #1
So this vent is from a water heater, viewed from the second story. It terminates 5 feet from this operable window and less than that from that wall to the right. From what I understood, the vent must terminate above the roof when less than 8 feet from the wall (I thought it was 5'), and then there is this window.
G2427.6.3 (503.6.4) Gas vent termination.
A gas vent
shall terminate in accordance with one of the following:
1. Gas vents that are 12 inches (305 mm) or less in size
and located not less than 8 feet (2438 mm) from a vertical
wall or similar obstruction shall terminate above
the roof in accordance with Figure G2427.6.3.
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
08-06-2010, 10:21 PM #2
Re: Wut's up with this vent?
Correct-- it can't be within 8' of the sidewall. When it gets extended, it must extend up a min. of 2' above the upper roof line as well.
08-07-2010, 07:21 AM #3
Interresting...you have to wonder how an entire housing track got away with this.
Thanks BW
08-07-2010, 09:00 AM #4
I believe you are not reading the correct code
2. Gas vents that are over 12 inches (305 mm) in size or(3048 mm) horizontally
are located less than 8 feet (2438 mm) from a vertical
wall or similar obstruction shall terminate not less
than 2 feet (610 mm) above the highest point where
they pass through the roof and not less than 2 feet (610
mm) above any portion of a building within 10 feet
08-07-2010, 09:37 AM #5
Over, under 12"...Isn't the vertical wall issue still applicable?
08-07-2010, 10:06 AM #6
08-07-2010, 10:13 AM #7
There is a difference
The photo shows it IS LESS than 8'
Since it IS LESS than 8', then rule 2 applies
08-07-2010, 02:03 PM #8
ooh yes, I had to read that twice and slowly. I hate the way code is written.