    Hey there, first time user.... curious to find out how much clearance should be maintained between fireplace direct vent and exterior stucco foam trim detail installed at the exterior of the home??

    Similar Threads:
    Inspection Referral

  2. #2
    Join Date
    Mar 2007
    Location
    Spring Hill (Nashville), TN
    Posts
    5,850

    Default Re: stucco foam clearance at fireplace direct vent

    Quote Originally Posted by Lawrence Carter View Post
    Hey there, first time user.... curious to find out how much clearance should be maintained between fireplace direct vent and exterior stucco foam trim detail installed at the exterior of the home??
    If you look at the vent pipe it should have printed on it the required distance for combustibles. Most I have seen have a shroud built around them that the cladding abuts up to.

    Scott Patterson, ACI
    Spring Hill, TN
    www.traceinspections.com

  3. #3
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Cool Re: stucco foam clearance at fireplace direct vent

    Stated clearances treat all combustibles the same whether wood, paper or foam so as Scott said, refer to the listed instructions or clearances marked on the venting. Note that many direct vent terminations are made in such a way that the unwary may not cut out enough combustibles allowing the pipe to get too close. Generally, there is an exterior firestop/ spacer installed first that ensures clearances then the termination mounts to this or is integral to it.

    Keep the fire in the fireplace.

  4. #4
    Join Date
    Sep 2008
    Location
    so so, California
    Posts
    1,873

    Default Re: stucco foam clearance at fireplace direct vent

    Did you get a pic?


  5. #5
    Join Date
    Jun 2010
    Location
    San Luis Obispo
    Posts
    26

    Default Re: stucco foam clearance at fireplace direct vent

    Item of note, many DV fireplaces set the vent clearance based on testing. So with many models, in the manual is the clearance for that fireplace and it's venting.

    For example a 20k btu valor with duravent DV venting may be different than a 45k btu Mendota fireplace also vented with Duravent DV.

    Just saying it's in the fireplace manual.
    my2c
    S


  6. #6
    Join Date
    Mar 2007
    Location
    Near Philly, Pa.
    Posts
    1,682

    Smile Re: stucco foam clearance at fireplace direct vent

    Quote Originally Posted by Stephen Tilleux View Post
    Item of note, many DV fireplaces set the vent clearance based on testing. So with many models, in the manual is the clearance for that fireplace and it's venting.

    For example a 20k btu valor with duravent DV venting may be different than a 45k btu Mendota fireplace also vented with Duravent DV.

    Just saying it's in the fireplace manual.
    my2c
    S
    Many DV fireplaces? Try ALL. It's part of the listing process through ANSI Z21.88

    Keep the fire in the fireplace.