10-04-2012, 10:25 PM #1
Need some help with this installation
Need some help with this repair. Left vertical is a vent right is to a tub. I wasn't sure if there is a clearance between the San T and vertical drain? Educate me, thanks.
Similar Threads:Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
10-05-2012, 03:26 AM #2
Re: Need some help with this installation
No problem with the clearance, but you have issues if the vent is supposed to be for the tub.
-
10-05-2012, 08:18 AM #3
Re: Need some help with this installation
my mistake, its not the tub...I'll re post when i remember what its for.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
10-05-2012, 08:20 AM #4
Re: Need some help with this installation
IRC 3005.1 & 706 - the sanitary Tee on the left side of the picture is not supposed to be installed on its' back.
-
10-05-2012, 08:29 AM #5
Re: Need some help with this installation
thanks Markus.
Last edited by Marc M; 10-05-2012 at 08:38 AM.
Mazza Inspections and stuff...
https://mazzainspections.com
https://waterintrusionspecialist.com
-
10-05-2012, 09:04 AM #6
Re: Need some help with this installation
-
10-05-2012, 02:01 PM #7
Re: Need some help with this installation
If left vertical is a vent as stated by OP, sanitary tee is allowed on its back as depicted. If left vertical is receiving discharge from any fixture, the tee would be incorrect.