Results 1 to 22 of 22
Thread: WIRE NUT DOUBLE TAPPING BREAKERS
-
04-17-2013, 01:39 PM #1
WIRE NUT DOUBLE TAPPING BREAKERS
GUYS
is it ok to wire nut three circuits to one breaker and i know the top wire nut has upper size wire nutted with smaller gauge wire. wrote it up to have repaired by licensed electrician. think i made right call--but can ammend report not due till tomorrow.
thjanks
cvf
Similar Threads:
-
04-17-2013, 02:30 PM #2
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Unless there is AL mixed with copper under the wire nut and the breaker size is appropriate there is no issue.
All answers based on unamended National Electrical codes.
-
04-17-2013, 02:53 PM #3
Re: WIRE NUT DOUBLE TAPPING BREAKERS
I would amend the report, unless there was a problem like those already posted.
-
04-17-2013, 03:10 PM #4
Re: WIRE NUT DOUBLE TAPPING BREAKERS
jack
ok to have two different size wires nutted together ?
cvf
-
04-17-2013, 03:39 PM #5
Re: WIRE NUT DOUBLE TAPPING BREAKERS
As long as the smallest or lowest rated wire is protected at its ampacity it is fine.
All answers based on unamended National Electrical codes.
-
04-17-2013, 04:37 PM #6
-
04-17-2013, 05:29 PM #7
Re: WIRE NUT DOUBLE TAPPING BREAKERS
That is the easy way to correct multiple tapped breaker terminals - connect the two-three-or more conductors to one new conductor with a properly sized wire nut connector and that one new conductor is then attached to the breaker.
Given the correct conditions stated above: i.e., the smallest conductor rating matches the breaker rating; rated for the proper wire sizes; etc.; then all is okay.
Also as stated in a post above, that is just one circuit.
-
04-17-2013, 07:20 PM #8
Re: WIRE NUT DOUBLE TAPPING BREAKERS
As long as the breaker is sized to the smallest conductor and the load doesn't exceed the breaker's handle rating your ok.
-
04-17-2013, 07:57 PM #9
Re: WIRE NUT DOUBLE TAPPING BREAKERS
ok thanks all got my answer
-
04-18-2013, 04:55 PM #10
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Whoa! Just to clarify this because your post was right below the post below: the breaker size is *not* sized to fixture wires from any fixtures, the breaker is sized to the branch circuit conductor size/rating.
Don't want someone to get the idea that the breaker needs to be sized to 16 AWG 18 AWG fixture wires.
-
04-19-2013, 06:37 AM #11
Re: WIRE NUT DOUBLE TAPPING BREAKERS
When does wire nutting multiple conductors together become an issue? I see where there is multiple instances of this in same panel. Why would you ever need to add a new panel if you could just keep adding conductors to existing breakers. I am not an electrician and am trying to learn for my clients benefit. Thanks for any advice.
-
04-19-2013, 08:33 AM #12
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Branch circuit wiring is rated for max distance for amperage of protection. Fixtures are rated differently and many times can utilize size smaller, very short distances so not much resistance, are designed and approved as such, etc. Circuit protection is more for the branch wiring in the structure to prevent overloading and causing fires, not so much for the protection of the device connected.
-
04-19-2013, 10:42 AM #13
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Tom, the issue would be if someone tried to run too much off of the circuit. Simply having a splice does not mean there is too much load connected. The loading could be the same with a single conductor attached as multiples spliced at the panel. The usage determines the loads, not the number of wires. A branch circuit could go in multiple directions from a device or junction box anywhere in the circuit.
Also certain circuits are required to be dedicated to certain areas and are not to be shared. Kitchen/dining receptacles, bathroom receptalces and laundry circuits are common ones.
All answers based on unamended National Electrical codes.
-
04-19-2013, 04:07 PM #14
Re: WIRE NUT DOUBLE TAPPING BREAKERS
"You got some 'splainin' to do ... " Huh?
No, the rating is not based on "max distance".
Fixtures are rated differently and many times can utilize size smaller, very short distances so not much resistance, are designed and approved as such, etc.
Circuit protection is more for the branch wiring in the structure to prevent overloading and causing fires, not so much for the protection of the device connected.
-
04-19-2013, 04:50 PM #15
-
04-19-2013, 05:01 PM #16
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Fixture wires are also sized based on the load expected to be imposed upon them.
All answers based on unamended National Electrical codes.
-
04-19-2013, 09:07 PM #17
Re: WIRE NUT DOUBLE TAPPING BREAKERS
-
04-20-2013, 05:02 AM #18
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Tom, besides what others have mentioned, one case where wire nutting multiple conductors in a service panel becomes a problem is when the max fill of the junction box (service panel in this case) is exceeded. This is usually not a problem in most newer panels, but could be a problem in some older panels that don't have much excess space to begin with.
-
04-21-2013, 07:24 AM #19
Re: WIRE NUT DOUBLE TAPPING BREAKERS
Would that not be in violation of using the panel board for a junction box? I understand the concept of using wire nuts in the panel board to extend wires or using them to correct double tapped overcurrent devices, but three wires to one seems like it would be using the panel board as a junction. Just curious.
-
04-21-2013, 08:42 AM #20
Re: WIRE NUT DOUBLE TAPPING BREAKERS
-
04-25-2013, 09:46 PM #21
Re: WIRE NUT DOUBLE TAPPING BREAKERS
write it up
-
04-27-2013, 09:57 AM #22
Bookmarks