Thread: AKA Sub-Panel
    Erwin, TN
    Default AKA Sub-Panel
    Looks like to me this 50 amp AKA detached garage sub-panel has the neutrals and grounds bonded together. If so this would be incorrect
    Default Re: AKA Sub-Panel
    Three wire feeders to outbuilding were allowed under the NEC as long as no metallic path existed between buildings. The neutrals and grounds were bonded like a service.
    Erwin, TN
    I thought on all downstream panels the neutral and ground had to be separated ? Is that with three wire and four service, has the code change now
    WESTMINSTER CO
    LOOKS to me they are on seperate bus bars--am I missing something
    cvfa
    The neutrals and grounds are on separate bars, The connector between the bars runs under the hot bus effectively making them the same.
    Three wire feeders to detached buildings were allowed as I said in post #2.
    That back fed main has no secondary hold down clamp or screw.
    That is correct ... except for detached buildings back when three conductor feeder with no ground were permitted - and only at the 'service equipment' panel at the detached building (I referred to it as the 'service equipment panel as the panel is required to be listed and labeled as "Suitable for use as service equipment" even though it is "not actually" "service equipment").
    With four wire (three plus a separate ground) feeders are installed the neutral is required to be isolated from ground at the detached buildings.