Results 1 to 7 of 7

Thread: AKA Sub-Panel

  1. #1
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default AKA Sub-Panel

    Looks like to me this 50 amp AKA detached garage sub-panel has the neutrals and grounds bonded together. If so this would be incorrect

    Similar Threads:
    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: AKA Sub-Panel

    Three wire feeders to outbuilding were allowed under the NEC as long as no metallic path existed between buildings. The neutrals and grounds were bonded like a service.

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Dec 2008
    Location
    Erwin, TN
    Posts
    330

    Default Re: AKA Sub-Panel

    I thought on all downstream panels the neutral and ground had to be separated ? Is that with three wire and four service, has the code change now

    - - - Updated - - -

    I thought on all downstream panels the neutral and ground had to be separated ? Is that with three wire and four service, has the code change now


  4. #4
    Join Date
    Apr 2007
    Location
    WESTMINSTER CO
    Posts
    1,153

    Default Re: AKA Sub-Panel

    LOOKS to me they are on seperate bus bars--am I missing something

    cvfa


  5. #5
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: AKA Sub-Panel

    The neutrals and grounds are on separate bars, The connector between the bars runs under the hot bus effectively making them the same.

    Three wire feeders to detached buildings were allowed as I said in post #2.

    All answers based on unamended National Electrical codes.

  6. #6
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: AKA Sub-Panel

    That back fed main has no secondary hold down clamp or screw.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

  7. #7
    Join Date
    Mar 2007
    Location
    Fletcher, NC
    Posts
    28,047

    Default Re: AKA Sub-Panel

    Quote Originally Posted by Sam Morris View Post
    I thought on all downstream panels the neutral and ground had to be separated ?
    That is correct ... except for detached buildings back when three conductor feeder with no ground were permitted - and only at the 'service equipment' panel at the detached building (I referred to it as the 'service equipment panel as the panel is required to be listed and labeled as "Suitable for use as service equipment" even though it is "not actually" "service equipment").

    Is that with three wire and four service, has the code change now
    With four wire (three plus a separate ground) feeders are installed the neutral is required to be isolated from ground at the detached buildings.

    Jerry Peck
    Construction/Litigation/Code Consultant - Retired
    www.AskCodeMan.com

Tags for this Thread

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •