Tapping conductors in the service
This is a 150amp service panel. They tapped the conductors to supply an auxiliary panel in the garge. The panel is rated for 125amp. Doesn't it have to be rated for 150amps?
Similar Threads:
-
05-15-2009, 12:39 PM #2
Re: Tapping conductors in the service
Presuming that means the main disconnect is rated for 150 amps.
They tapped the conductors to supply an auxiliary panel in the garge. The panel is rated for 125amp. Doesn't it have to be rated for 150amps?
Just as importantly, did you see what they did to the back of that service equipment enclosure?They really screwed that one up.
-
05-15-2009, 03:53 PM #3
Re: Tapping conductors in the service
You mean the hole they punched in the panel with the make shift bushing.
-