03-19-2009, 07:02 PM #1
Indoor and outdoor coils different manufacturer's
I am looking for some information on if the outdoor condenser and the indoor air handler should be the same manufacturer on a new construction home?
Also, I have come across some units installed in new construction without a filter/dryer on the liquid line. Is this acceptable?
Thank You
03-19-2009, 07:08 PM #2
Re: Indoor and outdoor coils different manufacturer's
The indoor coil needs to be matched, the AHU brand does not matter except for the appropriate CFM and physical size.
IF you have a factory charged line set, the lack of a dryer may not be significant, but if you see field assembled joints a dryer is required.
03-20-2009, 01:30 PM #3
Thanks Jim, that helps.
03-20-2009, 02:42 PM #4
More often than not, you will find the AHU 1 size larger than the condenser unit and usually this is acceptable. For specifics, consult the manufacturer. ie; up to 3.5 ton - AHUs may be .5 ton larger. 4 ton - 5 ton ahu ok.
03-22-2009, 09:04 PM #5
When units are installed after the original furnace instalation it is not uncommon to find a different evaporator manufature then the condensing unit, most often the installer tryes to find a coil that will match up with supply plenumn and the furnace opening. As stated the BTUH capacity which determines the CFM is the most important match up.