    Default Unconventional ground clamp
    The grounds are tucked out through a cable clamp. Is it wrong? Yes. How wrong is it?
    The tie-bar for two breakers is a galvanized nail. The breakers don't match, one is 15A the other is 20A, feeding a baseboard heater. Is it a hazard?
    The third beef is I couldn't view the main fuses, unable to open the door on the main disconnect panel.
    Default Re: Unconventional ground clamp
    John,
    It seems to me that the cable clamp is just that... a cable clamp. Not a grounding terminal.
    Yes, it is wrong.
    How wrong is it?
    It is very wrong.
    Wrong and wrong.
    Yes, the disconnect must be accessible.
    I've heard debate over this but - as far as I know, any splicing of the grounding conductor must be irreversible.
    Only the one from the service equipment to the first grounding electrode of the grounding electrode system. After that, any approved splice connection is acceptable, such as split bolt connectors.
    Thanks JP, so a split bolt would be an approved clamp for terminating the branch grounds?
    Is this something DIY's should learn?
    Should this be called a service disconnect panel, without the 'main' part?
    John,
    A split bolt is for 2 conductors, not a bunch of grounding conductors. The proper method would be to install an auxillary ground buss and terminate them there.
    What Jim said.
    Thank you Jim.
    How about running your ground wire to the hot water pipe coming out of the water heater.
    Michael Carson
    Inspect It Right Home Inspections L.L.C.
    www.inspectitrighthomeinspection.com
    Quote Originally Posted by Michael Carson View Post
    That would not be acceptable as you cannot be sure if the hot water pipe will contact ground. Are you sure that is not a bonding wire?