05-15-2013, 10:52 AM #1
Electrical Box & Drain pipe close together
Is there anything I can quote regarding the electric service and drain pipe being so close together? Thank in advance for any assistance
05-15-2013, 01:57 PM #2
Re: Electrical Box & Drain pipe close together
05-15-2013, 08:15 PM #3
This is the NEC code for the above drawings.
From the 2008 NEC:
- 110.26 Spaces About Electrical Equipment.
- - Sufficient access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
- - - (A) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1), (A)(2), and (A)(3) or as required or permitted elsewhere in this Code.
Table 110.26(A)(1)___|_______________________working Space
___________________|____________________Minimum Clear Distance
___________________|______________________________ ______________________________________
___________________|___Nom Voltage_____|_To Insulated___|__To Grounded_________|__To Live___
___________________|____To Ground______|___Surface_____|____Surface__________ _|___Parts____
___________________|__________________|___________ ____|_____________________|___________
___________________|______0-150________|____3 feet______|____3 feet____________|___3 feet___
___________________|_____151-600_______|____3 feet______|____3 feet 6 inches_____|___4 feet___
(note, other sub-sections are there, but the above apply to the table above)
05-16-2013, 06:40 AM #4
Correct.
That is because it looks like that pipe is out from the wall, not in the dedicated space against the wall, but ... it might be against the wall, in which case the dedicated space would be applicable.
I am going back and entering the text which precedes the table I entered in my previous post.
From the 2008 NEC:
- (continuing from my previous post)
- - (E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6½ ft). Where the electrical equipment exceeds 2.0 m (6½ ft) in height, the minimum headroom shall not be less than the height of the equipment.
- - - Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6½ ft).
- - (F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage.
- - - Exception: Control equipment that by its very nature or because of other rules of the Code must be adjacent to or within sight of its operating machinery shall be permitted in those locations.
- - - (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
- - - - - (a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
- - - - - - Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
- - - - - (b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
- - - - - (c) Sprinkler Protection. Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.
- - - - - (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.
- - - (2) Outdoor. Outdoor electrical equipment shall be installed in suitable enclosures and shall be protected from accidental contact by unauthorized personnel, or by vehicular traffic, or by accidental spillage or leakage from piping systems. The working clearance space shall include the zone described in 110.26(A). No architectural appurtenance or other equipment shall be located in this zone.
05-16-2013, 02:42 PM #5
Good job Robert. A picture is worth a thousand words.. Keep typing Jerry you have near 600 words left to catch up..
05-17-2013, 04:13 AM #6
It's interesting that the drawings do not show the minimum space required in front of the service panel. Actually that space is the most important when working on the equipment.
05-17-2013, 05:54 AM #7
05-17-2013, 06:41 AM #8
Actually the graphic is missing "something" to alert you to the requirement. Such as "See table xxx for working area". Or "36" minimum depending upon conditions". Or something.....
They went to a lot of trouble to identify the other space requirements, with a lot of detail---I just commented they failed to treat this area as well as others. As you see, when the graphic is removed from the table it is not useful in defining the requirements.