Results 1 to 3 of 3
  1. #1
    Join Date
    May 2009
    Location
    New Jersey
    Posts
    90

    Default This can't be right

    Am I missing something here? It looks to me that the two panels are sub-panels, however they were never wired that way.

    ***IMPORTANT*** You Need To Register To View Images ***IMPORTANT*** You Need To Register To View Images
    OREP Insurance

  2. #2
    Join Date
    Aug 2008
    Location
    Maryland
    Posts
    1,970

    Default Re: This can't be right

    The disconnect next to the extinguisher is the service panel. The others are just panels and should not have neutrals bonded to grounds.

    All answers based on unamended National Electrical codes.

  3. #3
    Join Date
    Mar 2007
    Location
    Lake Barrington, IL
    Posts
    1,367

    Default Re: This can't be right

    Did you open up the left panel to see what was inside?

    Eric Barker, ACI
    Lake Barrington, IL

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •