Results 1 to 13 of 13
08-23-2017, 10:02 AM #1
Black iron gas pipe through concrete
This is a black iron gas pipe in a garage. Meter is outside. Is there an issue with the concrete being in direct contact with the mortar? If so, is there a relatively easy fix or does the gas need to be shut off temporarily and the pipe removed to sleeve it?
If there is an issue, can you please include a code reference if one applies?
08-25-2017, 10:35 AM #2
Re: Black iron gas pipe through concrete
I see there has been no answer from the teeming masses. I do not recall any restriction based solely on the pipe penetrating through concrete, although a sleeve would be a good idea for a couple of reasons. I can see no evidence of excessive corrosion.
The only restriction that I recall is underground gas piping run through a foundation wall and/or a slab. Those are both covered in the UPC and IRC.
08-25-2017, 11:49 AM #3
That is the way I see it through stucco here on every house. I don't see a problem with it. Yes, under the slab is a big difference.
08-28-2017, 12:46 PM #4
Thank to those who responded. Her local gas company "black tagged" her meter (not sure what that means) after seeing this...I did the inspection months ago.
08-28-2017, 08:35 PM #5
08-29-2017, 06:19 AM #6
08-31-2017, 05:39 PM #7
08-31-2017, 07:11 PM #8
This is what I was thinking of:
(Borrowed from Jerry's post on another thread)P2603.4 Pipes through foundation walls.
A pipe that passes through a foundation wall shall be provided with a relieving arch or a pipe sleeve shall be built into the foundation wall. The sleeve shall be two pipe sizes greater than the pipe passing through the wall.
08-31-2017, 08:52 PM #9
09-01-2017, 01:26 PM #10
But ... but ... but ... that's not a "foundation wall".
Use one of the other references I posted for penetrations through exterior walls.
09-01-2017, 04:48 PM #11
09-01-2017, 05:21 PM #12
That is going through a block wall, from outside to inside into a garage, the meter is outside the wall - at least that is what the original post said.
That wall is no different than a block wall at the rear porch with a gas line going through it, or from outside to inside to a fireplace, or into a kitchen, etc.
09-10-2017, 05:58 PM #13
Should have a sleeve with the annular space sealed to prevent weather and rodent intrusion. It is in the NFGC and in the FG section of the plumbing codes. A poly spit sleeve is the easiest fix and a little silicone caulk. Hardest part is chipping out the mortar of what looks like a nice job.
to